We have two installations where a Growatt/Dyness system gets drained to below 20% and the system does not automatically start charging the battery the next morning even though there is good solar power available. The systems are as follows:

System #1
Growatt SPF5000es
Dyness A41100
8x Jinko Solar 580w panels

System #2
Growatt SPF6000es+
Dyness BX51100
10x Canadian Solar 550w

On both systems we have run into the issue, and a full system reset (ie switching off the solar, inverter, then battery) is needed for the inverter to charge the battery.

Both systems are on SUb priority and Li 52-36 program which has full communication to the Dyness BMS. System #1 exhibited this behaviour even though utility and solar was available. System #2 is was installed last week and had the same issue this morning although only solar was available..

Any suggestions welcome.
 
Last edited:
Because Dyness BMS will perform a hard disconnection at SOC of 20% and will not accept any charge/discharge unless if you do a BMS reset.

Solution, ensure the "Back to grid" at 25% to be safe and double ensure you have grid or generator?

Note: you can actually find the shut off SOC% at the Dyness manual/user guide, you know.....
 
Because Dyness BMS will perform a hard disconnection at SOC of 20% and will not accept any charge/discharge unless if you do a BMS reset.

Solution, ensure the "Back to grid" at 25% to be safe and double ensure you have grid or generator?

Note: you can actually find the shut off SOC% at the Dyness manual/user guide, you know.....
Thanks. However, this solution is likely to only work if there is grid available. It seems there isn't a setting on Growatt to cut-off at 25% in order to retain charge in the battery to allow automatic recharge once solar or grid returns. Grid power is only available for a few hours per day at most, some days there is no grid power available for extended periods.
 
Thanks. However, this solution is likely to only work if there is grid available. It seems there isn't a setting on Growatt to cut-off at 25% in order to retain charge in the battery to allow automatic recharge once solar or grid returns. Grid power is only available for a few hours per day at most, some days there is no grid power available for extended periods.
There is a setting in Growatt to disconnect the load which is Prog 21. Remember, there is a spread of 5% between Prog 12, 13 and 21.

If you set Prog 21 Low DC cut-off SOC to 25%, then automatically Prog 12 back to utility will be 30% and Prog 13 back to battery will be 35%.

However, you do realize the inverter get its "operating power" from the battery. The inverter needs power .......to produce power. Even if you disable the ac output/load at 25%, the inverter will still consume 50 - 60watts from the battery until it is depleted.
 
There is a setting in Growatt to disconnect the load which is Prog 21. Remember, there is a spread of 5% between Prog 12, 13 and 21.

If you set Prog 21 Low DC cut-off SOC to 25%, then automatically Prog 12 back to utility will be 30% and Prog 13 back to battery will be 35%.

However, you do realize the inverter get its "operating power" from the battery. The inverter needs power .......to produce power. Even if you disable the ac output/load at 25%, the inverter will still consume 50 - 60watts from the battery until it is depleted.
Thank you. I was unaware this could be set to % rather than voltage. Will have a look tomorrow.
 
Thank you. I was unaware this could be set to % rather than voltage. Will have a look tomorrow.

Voltage? You sure the BMS - Inverter comm is working? In BMS - Inverter comm mode, those Prog 12,13 and 21 will be shown in percentage instead of voltage.

Those are Growatt inverter settings, not Dyness BMS setting.............that 20% shut off SOC is hardcoded into Dyness BMS which you have no control over.
 
Voltage? You sure the BMS - Inverter comm is working? In BMS - Inverter comm mode, those Prog 12,13 and 21 will be shown in percentage instead of voltage.

Those are Growatt inverter settings, not Dyness BMS setting.............that 20% shut off SOC is hardcoded into Dyness BMS which you have no control over.
Yes, its working fine. I didn't touch Prog 12, 13, 21 as I wasn't aware one could adjust these when the BMS comms is working.
 
Hello. I have such a problem. Growatt SPF 6000 ES plus inverter and 4 HOPE 4.8 kWhr batteries are installed, there is no network, but there is a 5 kW generator. The batteries are very discharged and the inverter writes error 19. I can't charge them, neither from the generator nor from the solar panels.
 