New Member
We decided that the Richmond 10E65-HP5U15 65 gallon water heater would meet our off grid needs. It is a 240 volt 15 map heat pump water heater.
I ran a 10/3 romex to the box where the heater will sit. Once I got the heater box open I find that there are only 2 wires that are free for connection. There is a grounding lug, but no place for the neutral wire. This is a new construction metal building with interior wood framing, normal residential plumbing and electrical (for now).
My circuit breaker panel is N-G bonded and now I am not sure what to do. Should I attach the neutral to the ground lug at the water heater, or just let it float?
Background information.
Currently the electrical service has a meter and main disconnect at a utility pole 200 feet from the house. We buried conduit with three wires of 4/0 in size from there to a three pole manual transfer switch. The power then goes to a 200 amp circuit breaker panel with a 200 amp main cut off. I ran a seperate 4 AWG wire from the ground lug of the panel to the buried ground rods next to the house. I also screwed in the small green lug in the panel. I consider this to be the N-G bonding point. All GFCI outlets seem to test and reset fine.
Jeff
I ran a 10/3 romex to the box where the heater will sit. Once I got the heater box open I find that there are only 2 wires that are free for connection. There is a grounding lug, but no place for the neutral wire. This is a new construction metal building with interior wood framing, normal residential plumbing and electrical (for now).
My circuit breaker panel is N-G bonded and now I am not sure what to do. Should I attach the neutral to the ground lug at the water heater, or just let it float?
Background information.
Currently the electrical service has a meter and main disconnect at a utility pole 200 feet from the house. We buried conduit with three wires of 4/0 in size from there to a three pole manual transfer switch. The power then goes to a 200 amp circuit breaker panel with a 200 amp main cut off. I ran a seperate 4 AWG wire from the ground lug of the panel to the buried ground rods next to the house. I also screwed in the small green lug in the panel. I consider this to be the N-G bonding point. All GFCI outlets seem to test and reset fine.
Jeff