I thought I already said this.Understood on your concepts on devices being hosed for sure. I guess my question is if your devices (Inverter/SRR) were not protected internally and just fired, I assume this will create a short as well then blow the fuse even though its rated for way higher?
In a BMS protected system on a dead short the BMS usually disconnects first.
Then either the device fuse, branch fuse or battery fuse depending on the wire size and selective coordination.
Typically it can take a fuse up to 5 minutes to blow at 150% of their rating.
On a dead short the same fuse will blow in milli-seconds before the wire or the appliance will get noticably warm.
That is my story and I'm sticking to it.This is why nothing has ever been extremely problematic?
For me its not about un-wanted trips.So in a way:
sizing a breaker based on allowable wire load = protection for wire and less prone to unwanted trips while
sizing a breaker based on circuit load = Protection for the device but more prone to unwanted trips.
Higher rated fuses typically have lower resistance.
Its about not turning your very expensive DIY electricity into waste heat.
See above, my patience is wearing thin.So somewhere in the middle is best for devices not protected internally?
Yes, won't say it again.Anyway to not continue beating a dead horse you would recommend running fuses based on max wire capacity? which is 250A & 100A.