Help me diagnose my system

I don't think you have shared the sticker info from your panels.
But assuming the open circuit voltage is 40 volts you should see ~40 volts but 0 amps.
Unless you are using your meter in ampacity mode, is that what you are doing?
Yes.
 
Something odd there.
40v @ 10 amps would make these 400 watt panels.

How did you measure the current when you did your amperage test on the panels today?
I'll double check the sticker in the morning and send pics.
 
We need to know the bulk/absorb and float voltages.
Lithium is a bunch of different chemistries.
It may think you have a battery with max voltage of 12.6 volts.
That would not charge your lfp battery very quickly at all.

batteries, inverter, solar charge controller and the busbars that tie it together.
Will probably ask for wire guages after I see the picture.
The SCC has an option to manually set the charging levels.
I did so based on my batteries specs.

I'll send pics of all of that in the morning.
 
We need to know the bulk/absorb and float voltages.
Lithium is a bunch of different chemistries.
It may think you have a battery with max voltage of 12.6 volts.
That would not charge your lfp battery very quickly at all.

batteries, inverter, solar charge controller and the busbars that tie it together.
Will probably ask for wire guages after I see the picture.
Okay. Pics coming tomorrow evening.

Thanks a ton!
 
So you have 2s4p configuration for your panels, are you using combiner box or 4-to-1 adapter?
I also agree on testing one string string at a time to see if each string is putting out about the same or not.
 
so you have 2s4p configuration for your panels, are you using combiner box or 4-to-1 adapter.
I also agree on testing one string string at a time to see if each string is putting out about the same or not.
I'm using a 4 to 1 adapter.

I'll do the tests tomorrow and post pictures of every aspect of my system.

Thanks a ton for the help!
 
I just did a test like that today and I am getting 40 volts and 2 amps. I have tested each of my eight panels in this manner and the results are identical.
Then you should be getting 40 volts * 2 amps * 8 panels = 640 watts into the charge controller.
But you getting ~half that.
I love a good mystery.
 
30 feet give or take.
Assuming the pv wire is 10 awg if your panels delivered to spec your voltage drop should be slightly over 3 percent.
So your pv wires are not oversized.
I think someone mentioned testing each string separately. I'm curious to see the results.
 
Assuming the pv wire is 10 awg if your panels delivered to spec your voltage drop should be slightly over 3 percent.
So your pv wires are not oversized.
I think someone mentioned testing each string separately. I'm curious to see the results.
Yeah, I think the PV cables are 10AWG. After the 4 to 1 adapter I sized up to 2/0 for the run to the SCC. I don't remember why but it made sense at the time. :(

I'll confirm that in the morning.
 
Yeah, I think the PV cables are 10AWG. After the 4 to 1 adapter I sized up to 2/0 for the run to the SCC. I don't remember why but it made sense at the time. :(

I'll confirm that in the morning.
@McDubsy , you left us hanging.
 
I'd like to see the 4:1 adapter with 2/0 on the out

@McDubsy , you left us hanging.
Okay Fellas.
Here are the accurate specs. I was a bit off. :( I apologize for the bad lighting in the pics. They system is in the basement of my off grid cabin. This is all run similarly to the system that was here when I bought the place. I have simply been upgrading components. Once I get the system functioning properly, I will re-run the wiring.

Here is what I have.
*** 8 Trina Solar panels (Pic)
-325W
-VmP 37.2v
-ImP 8.73v
-VOC 45.6v
-ISC 9.19A
Panels are run in a 2s4p. The 4 in Parallel connect with a 4 to 1 adapter. From that they go to 6AWG to a fuse breaker switch, then from there to 2 AWG to the SCC about 30 feet away. If my math is correct, the max PV output is 74v-36.76a

*** I have a DC fuse breaker between the panels and SCC. (Pic)

*** Renogy Rover MPPT (Pic)
-Max PV input 150V
-Max PV input 100A

***I have a DC fuse breaker between the SCC and Batteries.(Pic)

*** Ampere Time batter bank. 2 12-300ah batteries in Parallel (Pic)

*** Renogy 2000W Inverter(Pic)
-I eventually need to upgrade to at least a 3000W inverter/charger So I can use my generator.

So this morning was cold and cloudy. Lots of ambient light but NO direct sun. The array was producing 300W. Which is very close to what it produces in full sun. (I'm confused) Am I REALLY losing THAT much due to the panel temperature?


So to recap my problem. I get an average of 350W from the panels in full sun. Average high is in the morning and is 500W. My SCC history shows it has gotten as high as 1200w only once.

I am open to ANY suggestions. I am happy to re-run anything or try different components. My fear is that the panels are faulty.

P.S.
I will test each pair of panels the next time I have a sunny day. (unless testing in the cloudiness would provide the needed info??)
 

Attachments

  • IMG_20220808_105411863_HDR.jpg
    IMG_20220808_105411863_HDR.jpg
    218.6 KB · Views: 13
  • IMG_20220808_105246694_HDR.jpg
    IMG_20220808_105246694_HDR.jpg
    90.1 KB · Views: 12
  • IMG_20220808_104749072_2.jpg
    IMG_20220808_104749072_2.jpg
    100.6 KB · Views: 12
  • IMG_20220808_104732763.jpg
    IMG_20220808_104732763.jpg
    105.6 KB · Views: 12
  • Rover 100.PNG
    Rover 100.PNG
    189.8 KB · Views: 15
  • IMG_20220808_104749072_3.jpg
    IMG_20220808_104749072_3.jpg
    104.1 KB · Views: 14
  • IMG_20220808_104805780.jpg
    IMG_20220808_104805780.jpg
    104.9 KB · Views: 14
  • IMG_20220808_104717781.jpg
    IMG_20220808_104717781.jpg
    98.4 KB · Views: 14
I will test each pair of panels the next time I have a sunny day. (unless testing in the cloudiness would provide the needed info??)
It might be elucidating.
I say go for it.

Is that car audio cable on the pv run?
I see you are tapping only one end of the battery.
That usually results in uneven charger/discharge between the batteries.
 
It might be elucidating.
I say go for it.

Is that car audio cable on the pv run?
I see you are tapping only one end of the battery.
That usually results in uneven charger/discharge between the batteries.
Okay. I will test the panels.

Yes that is audio wire. I had forgotten about that. I have the correct stuff. I'll swap it out.

By tapping, are you referring to my little clamp on the left positive terminal? That is from an AC charger that I am not running at the moment.
 
Okay. I will test the panels.

Yes that is audio wire. I had forgotten about that. I have the correct stuff. I'll swap it out.

By tapping, are you referring to my little clamp on the left positive terminal? That is from an AC charger that I am not running at the moment.
No I mean the main system wires.
For batteries in parralel the diagonal pattern is better.
See page 18 of wiring unlimited. -- https://www.victronenergy.com/upload/documents/Wiring-Unlimited-EN.pdf

Never mind I just don't see well.
 