I recently purchased the PowMr Sunsmart 5k hybrid AIO for my off-grid install. I DO NOT have a N-G bond at main. I got everything installed and it seems to be powering things without issue but while I was testing the AC-Out and AC-in terminals I got some strange reading with my DMM. Even stranger, I was detecting DC voltage on the AC-In and AC-out terminals. Let me start by saying I've verified the measurements with 2 other DMMs including a Fluke and Klein tools which are tested and proven units so it's not an issue with the tool.
Ill also link a few videos of me taking these measurements
Note: AC-in didnt have anything connected to it when I first got these readings. I thought it might be a grounding issue where the inverter builds but static voltage so I ran my EGC #6 wire from ground rod directly to the G terminal of AC-In but it didn't change anything.
Note2: Measurements were taken at night with PV disconnect on/closed, then repeated with disconnect off/open with identical results.
Note3: I have 2x 48V batteries wired in parallel powering the inverter
Note4: Don't think it's relevant but if anyone wants to know I have 9x 320w panels wired in series with a VOC of approx 400VDC.
AC OUT (Feeding my panel via 63A breaker)
N-G : 29-37 VAC /// 99VDC
L-N : 120 VAC /// 0VDC
L-G : 87-96VAC /// 100VDC
AC IN ( No connections except EGC to G.)
N-G : 29 VAC /// 99VDC
L-G : 29 VAC /// 99VDC
L-N : 0 VAC /// 3VDC
PV Input (PV wires disconnected)
33-34 VDC
Can anyone make any sense of this for me please? I've been going back and forth with their tech department for a couple weeks now and I keep getting the run-around.
Link to the videos: https://drive.google.com/drive/folders/1m2gSEpKw3DT7hmtL-xyl97h1nST1d-oH
The 4min video shows all the readings mentioned above.
Ill also link a few videos of me taking these measurements
Note: AC-in didnt have anything connected to it when I first got these readings. I thought it might be a grounding issue where the inverter builds but static voltage so I ran my EGC #6 wire from ground rod directly to the G terminal of AC-In but it didn't change anything.
Note2: Measurements were taken at night with PV disconnect on/closed, then repeated with disconnect off/open with identical results.
Note3: I have 2x 48V batteries wired in parallel powering the inverter
Note4: Don't think it's relevant but if anyone wants to know I have 9x 320w panels wired in series with a VOC of approx 400VDC.
AC OUT (Feeding my panel via 63A breaker)
N-G : 29-37 VAC /// 99VDC
L-N : 120 VAC /// 0VDC
L-G : 87-96VAC /// 100VDC
AC IN ( No connections except EGC to G.)
N-G : 29 VAC /// 99VDC
L-G : 29 VAC /// 99VDC
L-N : 0 VAC /// 3VDC
PV Input (PV wires disconnected)
33-34 VDC
Can anyone make any sense of this for me please? I've been going back and forth with their tech department for a couple weeks now and I keep getting the run-around.
Link to the videos: https://drive.google.com/drive/folders/1m2gSEpKw3DT7hmtL-xyl97h1nST1d-oH
The 4min video shows all the readings mentioned above.