I use a Victron Smartshunt connected to SA. If you can't tell bulk from float when viewing the graphs, well, it is kinda like this whole thread. (The inverters do float charge)
What you wish for doesn't probably exist simply due to the inverter not having the output to indicate bulk or float to SA.
Solar Assistant does request data from Modbus-RTU Register 0x10B ( Battery_Charge_State). SA does not do anything with it. Don't know if SA makes it available via MQQT
This is a sequence of commands sent by SA to the SRNE Inverter and the data in the response
Command: 01-03-00-1B-00-01-F4-0D
Registers: 0x1B 0x1B 1
Register: 0x1B Model_Code
Raw Register Data: 00-22
Response: 01-03-02-00-22-38-5D
Command: 01-03-02-04-00-1F-44-7B
Registers: 0x204 0x222 31
Register: 0x204 Current_Fault_Code1
Raw Register Data: 00-00
Register: 0x205 Current_Fault_Code2
Register: 0x206 Current_Fault_Code3
Register: 0x207 Current_Fault_Code4
Register: 0x208 Reserved_0X0208
Register: 0x209 Reserved_0X0209
Register: 0x20A Reserved_0X020A
Register: 0x20B Reserved_0X020B
Register: 0x20C System_Current_Date_Time
Raw Register Data: 19-05-07-16-07-0C
Register: 0x20F Grid_On_Remain_Time
Register: 0x210 Current_Inverter_State
Raw Register Data: 00-05
Register: 0x211 Password_Protection_Status_Mark
Register: 0x212 Inverter_Bus_Voltage
Raw Register Data: 0F-20
Register: 0x213 Grid_Voltage_Phase_A
Register: 0x214 Grid_Current_Phase_A
Register: 0x215 Grid_Frequency
Register: 0x216 Inverter_Voltage_Phase_A
Raw Register Data: 04-B0
Register: 0x217 Inverter_Current_Phase_A
Raw Register Data: 00-0F
Register: 0x218 Inverter_Frequency
Raw Register Data: 17-6E
Register: 0x219 Load_Current_Phase_A
Raw Register Data: 00-0C
Register: 0x21A Load_Power_Factor
Register: 0x21B Load_Active_Power_Phase_A
Raw Register Data: 00-8D
Register: 0x21C Load_Apparent_Power_Phase_A
Raw Register Data: 00-90
Register: 0x21D Inverter_DC_Component
Register: 0x21E Charge_Current_From_Grid
Register: 0x21F Load_Ratio_Phase_A
Raw Register Data: 00-02
Register: 0x220 Temperature_DC
Raw Register Data: 01-3E
Register: 0x221 Temperature_AC
Raw Register Data: 01-96
Register: 0x222 Temperature_TR
Raw Register Data: 02-49
Response: 01-03-3E-00-00-00-00-00-00-00-00-00-00-00-00-00-00-00-00-19-05-07-16-07-0C-00-00-00-05-00-00-0F-20-00-00-00-00-00-00-04-B0-00-0F-17-6E-00-0C-00-00-00-8D-00-90-00-00-00-00-00-02-01-3E-01-96-02-49-5A-28
Command: 01-03-01-00-00-10-45-FA
Registers: 0x100 0x10F 16
Register: 0x100 Battery_SOC
Raw Register Data: 00-13
Register: 0x101 Battery_Voltage
Raw Register Data: 02-06
Register: 0x102 Battery_Current
Raw Register Data: 00-25
Register: 0x103 Inverter_Battery_Temperatures
Register: 0x104 Load_DC_Voltage
Register: 0x105 Load_DC_Current
Register: 0x106 Load_DC_Power
Register: 0x107 PV_Panel_1_Voltage
Register: 0x108 PV_Panel_1_Current
Register: 0x109 PV_Panel_1_Power
Register: 0x10A DC_Load_On_Off_Command
Register: 0x10B Battery_Charge_State
Register: 0x10C Controller_Failure_Alarm_Message
Raw Register Data: 00-00-00-00
Register: 0x10E Total_Battery_Charge_Power
Register: 0x10F PV_Panel_2_Voltage
Response: 01-03-20-00-13-02-06-00-25-00-00-00-00-00-00-00-00-00-00-00-00-00-00-00-00-00-00-00-00-00-00-00-00-00-00-5E-00
Command: 01-03-E0-01-00-05-E3-C9
Registers: 0xE001 0xE005 5
Register: 0xE001 Max_PV_Charger_Current
Raw Register Data: 00-0A
Register: 0xE002 Nominal_Battery_Capacity
Raw Register Data: 00-64
Register: 0xE003 System_Voltage_Rate_Read_Only
Raw Register Data: 00-30
Register: 0xE004 Battery_Type
Raw Register Data: 00-06
Register: 0xE005 Battery_Overcharge_Voltage_Protection
Raw Register Data: 00-96
Response: 01-03-0A-00-0A-00-64-00-30-00-06-00-96-5F-BB
Command: 01-03-E0-06-00-0B-D3-CC
Registers: 0xE006 0xE010 11
Register: 0xE006 Battery_Limited_Charge_Voltage
Register: 0xE007 Battery_Equalization_Charge_Voltage
Raw Register Data: 00-8C
Register: 0xE008 Battery_Boost_Charge_Voltage
Register: 0xE009 Battery_Floating_Charge_Voltage
Register: 0xE00A Battery_Charge_Recovery_Voltage
Raw Register Data: 00-86
Register: 0xE00B Battery_Undervoltage_Recovery_Voltage
Raw Register Data: 00-82
Register: 0xE00C Battery_Under_Voltage_Warning_Alarm
Raw Register Data: 00-7C
Register: 0xE00D Battery_Over_Discharge_Voltage
Raw Register Data: 00-70
Register: 0xE00E Battery_Discharge_Limit_Voltage
Raw Register Data: 00-6C
Register: 0xE00F Battery_Charge_Cutoff_SOC
Raw Register Data: 00-0E
Register: 0xE010 Battery_Over_Discharge_Delay_Time
Raw Register Data: 00-1E
Response: 01-03-16-00-90-00-8C-00-8C-00-8C-00-86-00-82-00-7C-00-70-00-6C-00-0E-00-1E-5B-81
Command: 01-03-E0-11-00-13-63-C2
Registers: 0xE011 0xE023 19
Register: 0xE011 Battery_Equalized_Time
Register: 0xE012 Battery_Boost_Charge_Time
Raw Register Data: 00-78
Register: 0xE013 Battery_Equalization_Interval
Register: 0xE014 Battery_Temperature_Compensation_Coefficient
Register: 0xE015 Battery_Charge_Upper_Limit_Temperature
Raw Register Data: 00-3C
Register: 0xE016 Battery_Charge_Lower_Limit_Temperature
Raw Register Data: FF-E2
Register: 0xE017 Battery_Discharge_Upper_Limit_Temperature
Register: 0xE018 Battery_Discharge_Min_Temperature
Register: 0xE019 Battery_Heater_Start_Temperature
Register: 0xE01A Battery_Heater_Stop_Temperature
Register: 0xE01B Battery_To_Grid_Switching_Voltage
Raw Register Data: 00-7B
Register: 0xE01C Battery_Stop_Charging_Current
Raw Register Data: 00-14
Register: 0xE01D Battery_Charging_Cutoff_SOC
Register: 0xE01E Battery_Discharging_SOC_Alarm
Register: 0xE01F Switch_To_Grid_SOC
Register: 0xE020 Switch_To_Battery_SOC
Register: 0xE021 Battery_Hybrid_Discharge_Current
Raw Register Data: 03-E8
Register: 0xE022 Inverter_Switching_Voltage
Register: 0xE023 Battery_Equalized_Time_Out
Response: 01-03-26-00-05-00-78-00-05-00-05-00-3C-FF-E2-00-3C-FF-E2-00-00-00-05-00-7B-00-14-00-64-00-0F-00-14-00-64-03-E8-00-90-00-0A-47-48
Command: 01-03-E2-00-00-02-F2-73
Registers: 0xE200 0xE201 2
Register: 0xE200 RS485_Address
Raw Register Data: 00-01
Register: 0xE201 Parallel_Mode
Response: 01-03-04-00-01-00-00-AB-F3
Command: 01-03-E2-04-00-10-33-BF
Registers: 0xE204 0xE213 16
Register: 0xE204 Output_Priority
Register: 0xE205 Max_Grid_Charger_Current
Raw Register Data: 01-18
Register: 0xE206 Battery_Equalization_Enable
Register: 0xE207 NPE_Ground_Bonding_Connect
Register: 0xE208 Inverter_Output_Voltage_Setting
Register: 0xE209 Inverter_Output_Frequency_Setting
Raw Register Data: 17-70
Register: 0xE20A Max_Battery_Charge_Current
Raw Register Data: 01-2C
Register: 0xE20B Grid_Input_Voltage_Range
Register: 0xE20C Power_Saving_Mode
Register: 0xE20D Restart_When_Over_Load
Register: 0xE20E Restart_When_Over_Temperature
Register: 0xE20F Charger_Source_Priority
Register: 0xE210 Alarm_Enable
Register: 0xE211 Input_Change_Alarm
Register: 0xE212 Bypass_Output_When_Over_Load
Register: 0xE213 Record_Fault_Code
Response: 01-03-20-00-02-01-18-00-00-00-00-04-B0-17-70-01-2C-00-01-00-00-00-01-00-01-00-02-00-01-00-01-00-01-00-01-F5-49
Command: 01-03-E2-14-00-02-B2-77
Registers: 0xE214 0xE215 2
Register: 0xE214 BMS_Shutdown_Enabled
Register: 0xE215 BMS_Communication_Enable
Response: 01-03-04-00-00-00-01-3B-F3
Command: 01-03-E2-1B-00-01-C2-75
Registers: 0xE21B 0xE21B 1
Register: 0xE21B BMS_Protocol
Raw Register Data: 00-08
Response: 01-03-02-00-08-B9-82
Command: 01-03-DF-00-00-0E-FF-DA
Registers: 0xDF00 0xDF0D 14
Register: 0xDF00 Power_ON_OFF_Control
Register: 0xDF01 Reset_Control
Register: 0xDF02 Restore_To_Default_Settings
Register: 0xDF03 Clear_Current_Alarm
Register: 0xDF04 Clear_Statistics
Register: 0xDF05 Clear_History
Register: 0xDF06 Firmware_Upgrade_Command
Register: 0xDF08 Sleep_Control_Activation_Command
Register: 0xDF09 Manual_Light_Up_Switch
Raw Register Data: 00-00-00-00-00-00
Register: 0xDF0C Generator_Switch_Command
Register: 0xDF0D Battery_Equalization_Immediately
Response: 01-03-1C-00-01-00-00-00-00-00-00-00-00-00-00-00-00-00-00-00-00-00-00-00-00-00-00-00-00-00-00-A2-27
Command: 01-03-00-21-00-14-15-CF
Registers: 0x21 0x34 20
Register: 0x21 Software_Compile_Time
Raw Register Data: 00-4F-00-63-00-74-00-20-00-31-00-32-00-20-00-32-00-30-00-32-00-34-00-20-00-31-00-37-00-3A-00-35-00-30-00-3A-00-34-00-30
Response: 01-03-28-00-4F-00-63-00-74-00-20-00-31-00-32-00-20-00-32-00-30-00-32-00-34-00-20-00-31-00-37-00-3A-00-35-00-30-00-3A-00-34-00-30-62-2B
Command: 01-03-00-35-00-14-55-CB
Registers: 0x35 0x48 20
Register: 0x35 Product_SN_String
Raw Register Data: 00-53-00-52-00-2D-00-32-00-34-00-31-00-32-00-32-00-32-00-30-00-30-00-34-00-31-00-2D-00-33-00-30-00-31-00-38-00-32-00-37
Response: 01-03-28-00-53-00-52-00-2D-00-32-00-34-00-31-00-32-00-32-00-32-00-30-00-30-00-34-00-31-00-2D-00-33-00-30-00-31-00-38-00-32-00-37-4F-F7
Command: 01-03-00-14-00-09-C5-C8
Registers: 0x14 0x1C 9
Register: 0x14 Software_Version
Raw Register Data: 00-E7-00-C9
Register: 0x16 Hardware_Version
Raw Register Data: 00-C8-00-00
Register: 0x18 Product_SN
Register: 0x1A RS485_Address_Read_Only
Register: 0x1C RS485_Protocol_Version
Raw Register Data: 00-6B-00-00
Response: 01-03-14-00-E7-00-C9-00-C8-00-00-00-00-00-00-00-01-00-22-00-6B-00-00-76-E6
Command: 01-03-E1-18-00-01-32-31
Registers: 0xE118 0xE118 1
Register: 0xE118 Power_Rate
Raw Register Data: 00-32
Response: 01-03-02-00-32-39-91