I bought a klein rt250 tester and I can't figure out why its showing the error its showing.

Shows hot/grd reversed and it shows 30 volts.

Everything working fine in the house. Also all outlets check out at 120v using a voltmeter.

If I put one of those 3 to 2 prong adapters on it the tester shows 120v and open ground.

I even tested it on a circuit that comes straight off the inverter. Same results.

I visually verified that outlet had an L1, neutral and ground running directly to the L1, neutral and ground on the inverters lugs.


Suggestions?
 
Perhap
I bought a klein rt250 tester and I can't figure out why its showing the error its showing.

Shows hot/grd reversed and it shows 30 volts.

Everything working fine in the house. Also all outlets check out at 120v using a voltmeter.

If I put one of those 3 to 2 prong adapters on it the tester shows 120v and open ground.

I even tested it on a circuit that comes straight off the inverter. Same results.

I visually verified that outlet had an L1, neutral and ground running directly to the L1, neutral and ground on the inverters lugs.


Suggestions?
S thw neutral isnt ground referenced, or a bonding issue is present?
 
Later today I'm going to try turning off the main breaker that feeds the house from the inverter and leave the outlets right at the inverter turned on and see if I get the same weird readings.
 
Could check the tester somewhere else entirely. A friend's house.
Well there is a problem with that. All of the houses close by including the two homes I own that are side by side are from the early 60's and older. All of them are wired with no grounds. Just hot and neutral. So its kind of impossible to test most of the outlets since they don't have a ground wire connected at the outlets :)

My main house has a few outlets that were done during renovations and I have run a few new circuits. Those have a ground wire and have the listed symptoms. But those same circuits are on the solar side wiring wise. Older outlets don't have a ground so they don't show issues with the tester.
 
I bought a klein rt250 tester and I can't figure out why its showing the error its showing.

Shows hot/grd reversed and it shows 30 volts.

Everything working fine in the house. Also all outlets check out at 120v using a voltmeter.

If I put one of those 3 to 2 prong adapters on it the tester shows 120v and open ground.

I even tested it on a circuit that comes straight off the inverter. Same results.

I visually verified that outlet had an L1, neutral and ground running directly to the L1, neutral and ground on the inverters lugs.


Suggestions?
With your voltmeter test hot to neutral, hot to ground, neutral to ground. Than start unplugging things and do testing.
 
The 30vac could be a reference to the voltage the gfci tester is using in an attempt to "trip" the circuit, when you use the 2 prong attachment, it reads correctly with open grnd as there is no grnd to use to try to trip gfci outlet
 
When you use the two prong adapter, it has no ground reference to determine which is hot or neutral. All that it can tell you is that 120V is present, but not if the "polarity" is correct.
 
High end furnace computer boards require ground, and neutral in corect hot polarity for the flame sense to work right, so i see this all the time.
 
K, just a question, as I’m trying to learn here, why do 2 hots read 220 with no neutral, but if a “neutral went hot” would it not read higher voltage?
Because in this case it would just be a reversal of a hot and neutral.
To get 240v, you need one hot from each leg.
The neutral is the center point between the two legs. Which is why it's only one half of the voltage.
 
Backfeeding is the wrong term being used by myself then, I will do more research to use correct terminology, was voltage coming in on both hots and the neutral from hydro transformer, apologies to the op for highjacking their thread
 