Where is "1-5 A"?
Type J
"Ratings • Volts • 600Vac (or less) • 450Vdc (or less, 15-600A) • Amps 1-600A • IR • 200kA RMS Sym. • 100kA DC"
CHSF
"Ratings • Volts - 500Vac/dc • Amps – 50-400A • Interrupting rating • Max AC – 200kA • Min AC 400% • Max DC – 50kA • Min DC 800%"
50kA or 100kA good for LiFePO4 banks with multiple cell strings.
Previously I was considering 4p16s (which could need such a fuse), but I do have concerns about individual cells sucking current not able to be isolated by BMS.
Now I'm thinking 16s4p, each 16s with its own BMS.
In that case, one 200A class T fuse per string of cells.
Combine with busbar.
Separate 2/0 wires to each inverter, not protected at near end (and 4p separate fuses don't protect against overload) but protected by 125A breaker in inverter.
In the event of a short, the 4 parallel fuses could deliver 800A but if 2/0 cable gets shorted it will fast-blow the fuse.
Type J
"Ratings • Volts • 600Vac (or less) • 450Vdc (or less, 15-600A) • Amps 1-600A • IR • 200kA RMS Sym. • 100kA DC"
CHSF
"Ratings • Volts - 500Vac/dc • Amps – 50-400A • Interrupting rating • Max AC – 200kA • Min AC 400% • Max DC – 50kA • Min DC 800%"
50kA or 100kA good for LiFePO4 banks with multiple cell strings.
Previously I was considering 4p16s (which could need such a fuse), but I do have concerns about individual cells sucking current not able to be isolated by BMS.
Now I'm thinking 16s4p, each 16s with its own BMS.
In that case, one 200A class T fuse per string of cells.
Combine with busbar.
Separate 2/0 wires to each inverter, not protected at near end (and 4p separate fuses don't protect against overload) but protected by 125A breaker in inverter.
In the event of a short, the 4 parallel fuses could deliver 800A but if 2/0 cable gets shorted it will fast-blow the fuse.