I think grounding is necessary if you're using RCDs
There are a few scenarios where an RCD/GFCI would still trip without an earth ground....They all center on power going from the hot wire to the equipment grounding system (The 'ground wire') that is not connected to earth ground. However, it is also true that there are a lot of cases that are not covered if there is no earth ground.I think grounding is necessary if you're using RCDs
Following this thread myself with my GroWattSPF3000. I don't have the GW grounded directly, don't think there is an option/lug for it. However, I do have it connected to grid via AC IN with Hot/Neutral/Ground. Testing output from device with an open ground plug tester, everything seems to be fine (according to $10 tester from Home Depot) in both direct grid power mode and inverter mode to AC OUT.Anyone do the testing for any of the GroWatt inverters yet?
From what I’m seeing, I should take the grounding lug to my earth ground . Thanks for all the time and effort you put into this forum. Your my go to guy for straight information
Another popular inverter (only because of the cheap price) is the high-frequency Reliable WZRELB. Most will measure a floating 60V hot-ground and 60V neutral-ground, as was tested on my 48V 2500W.Same problem here, just got my new AIMS 48v 6000w inverter last night, hooked it up, saw the open ground. So I thought, oh I'll just bond the ground-neutral externally. Emailed Aims to make sure that's okay, and good thing I did because I got this reply:
"You CAN NOT bond the neutral and ground on this inverter as it is a high frequency style inverter and creates 60V on the neutral and 60V on the hot line. Bonding these will force the power to the hotline and cause damage to the inverter that is not covered under warranty."
So now I have to waste hundreds of $$$ on shipping and "restocking fees" to return this garbage, and get something with a real 120 hot wire, and that can be bonded properly.
Another popular inverter (only because of the cheap price) is the high-frequency Reliable WZRELB. Most will measure a floating 60V hot-ground and 60V neutral-ground, as was tested on my 48V 2500W.
Yeah, could be. What I didn't mention in my original comment (or to AIMS) was that I actually *did* bond its ground and neutral and ran it for a while. It seemed fine. But after I getting their dire earnings against it, I decided I didn't want to deal with it blowing up at some later point and them not covering the warranty.Maybe AIMS felt the connection sequence would be a liability.
The second diagram makes sense to me: during inverter mode (power from battery), your device automatically completely disconnects from all house AC sources, for obvious reasons (although it's weird that the cartoon doesn't show a battery anywhere).why the bond "oscillates" between AC-IN and AC-OUT terminals
Are you sure that those measurements are in the correct places. N/G bonding should take place in battery mode and not in bypass mode. According to your picture, it's the opposite.Ok... let me try to explain a little bit more:
1. The image is drawn by me and is really over-simplified, I just wanted to have illustration of "complete circuit", but really just wanted to focus on the inverter terminals.
2. I live in Bulgaria and here our old houses have "two wires" installations from the MAINS (L and N, just one 230V phase), and that is why the drawing between inverter (near the MAINS) and the "OLD ENCLOSURE" (in the house) is indicating only two wires (I need to reroute another grounding wire.. I get it, but it's not subject of my question/problem). Also, there is a grounding rod before the MAINS enclosure, directly connected to the N (in the enclosure provided by the electricity distribution company)
3. From now on, lets assume that my MAINS AC is 3-wire and also my house enclosure is also 3-wire and everything is "perfect" outside of the inverter.
4. Lets just focus on the inverter terminals and the N-G bonding's in it, which worries me and are the general subject of my posting.
Here is a drawn by me illustration of the method which I used to conclude the internal bonding of the terminals on the inverter.
Please note - in this scenario I have connected wires L and N from the mains ONLY (without grounding, so it won't "bond" on the multimeter from the mains)
View attachment 86865
Are you sure that those measurements are in the correct places. N/G bonding should take place in battery mode and not in bypass mode. According to your picture, it's the opposite.
This can be a great resource. We would like an index that links to the inverter information without scrolling many many many posts.Folks, When setting up an inverter, one of the more important safety things to get correct is the grounding and the neutral-Ground bond.
Sadly, the information provided in many manuals is nearly non-existent when it comes to how it handles ground internally.
- All of the inverters have a grounding lug
- All of the inverters have a ground connection on the AC out.
- Some inverters have an AC in and when they do they have a ground connection on the input.
Are the two (or three) grounds tied together?
Is there a neutral-ground bond?
If there is an AC-IN, does it change the neutral-ground bond when getting power from the AC-in?
I have started to try and collect this type of information for various inverters. Once I get information on several of them I will put it all into a resource and post it.
How does your inverter handle internal ground? If you send me the make/model of your inverter, I will add it to the resource.
The next 3 posts are examples of what I envision for each page of the resource.
I have not updated it in a while but.....This can be a great resource. We would like an index that links to the inverter information without scrolling many many many posts.
I have the EPEVER UP5000 M3842, and it has the same lack of Neutral grounding.EPEVER UP3000-HM10022
Hybrid Inverter
Just Been through this exact same senario with Epever, initially contacted them about their output Neutral Ground /Earth bonding and after confirming its suitability i found out that infact when supplied by a Mains TNC-S supply( Neutral Earthing bond at the Main switchboard ) operating in Bypass Mode the earthing system configuration passes through to the output correctly', but when placed in inverter mode the inverter output creates an IT system /isolated supply -unbonded system , therefor in Australia the outputs downstream RCD protection would not be configured correctly for correct operation as its looking for a TNC-S supply
In simple terms the output should be neutral earth bonded but cannot be because when in bypass it already is and then placing a second neutral earth bond at the output places this in parallel to the first, should the inverter supply be by a RCD / GFCI circuit then nuisance tripping will occur whilst protective earth would share load current with the neutral that's not permitted
So moral to this story , understand your local standards and the accepted earthing system to be employed , because there are a multitude of earthing systems and the language varies by country , ie GFCI,RCD, Neutral Earth Bonded, MEN system , TNC, TNCS , IT , Earthing Conductor , Grounding Conductor, being very clear with your inverter supplier of what you require in the manuals i have read, this topic is definitely not clear when you start dealing with Clone type inverters and Languages or in Australia we say the Lingo
The solution to the above is now not that easy , an inverter with a configurable earthing system is what's required or a system as shown in filter guys inverter drawings where the output is automatically reconfigured, please look at the variances and i congratulate the Filter Guy for trying to clarify and hope i have added some further incite