Roswell Bob
Solar Enthusiast
Does anyone know how the bus capacitance of an inverter is chosen? I have been told that a 6kW inverter should have 0.1F from one source, and 0.028F from another source.
Does anyone know how the bus capacitance of an inverter is chosen? I have been told that a 6kW inverter should have 0.1F from one source, and 0.028F from another source.
I am curious: Why do you ask?Does anyone know how the bus capacitance of an inverter is chosen? I have been told that a 6kW inverter should have 0.1F from one source, and 0.028F from another source.
I am not a fan of HF hybrid inverters, but you got me curious on how much help the HV DC filter cap will do.Also, high frequency inverters, that store energy on their high voltage link rails, tend to have less 120 Hz battery side ripple so that can help their battery side ripple that can cause the battery cable L-C resonance issues and high voltage peaks on their low voltage input stages.
Yes, the HV output sinewave PWM devices maybe IGBT's. Same thing, only differentI thought that looked like an MPP inverter !
Looks like they have possibly reduced the complexity a bit but it is kind of hard to tell.
Does they still use a separate charger from the inverter to go from HV to 48V ?
Are you sure that the inverter sinewave PWM section is MOSFETs and not IGBTs ? I think that's what they used to use but the one I looked at was from like, 5 years ago and was 230VAC 50Hz only.
The HV capacitors help reduce 48V ripple but maybe only about 1/3rd or so of what it would be at those microfarads. Any reduction is better than nothing.
boB
I have done motor drives where the primary concern is ripple current - a good portion of the ripple current is from the input side. Capacitors were for the most part chosen to deal with the ripple current. How long would they last was our main concern. The actual capacitance was not so important-we bought caps for ripple current capability. Over the years capacitor technology improved with higher ripple ratings per volume.I am curious: Why do you ask?
Yes low inductance bus structures are very important. DRC snubbers do a nice job taking care of the ringing. Maybe best approach is to mount switches directly on top of cells. A filter inductor between cell array and inverter bus might be a good strategy if the intent is to get rid of any 60Hz. I did quick simulation of 7.5HP unloaded motor on .028F bus and saw about 4v pk-pk on the caps. Not bad. I will look at current into the cells. Yes, electrolytic caps can take pretty much whatever you can throw at them- no prob. Yes, a single mosfet can charge a very large bus without a resistor if it is turned on in a particular manner. I wonder what the BMS I a putting into my system is using for start-up. Good points - thanks.If by bus capacitance you are referring to battery DC input to inverter, the purpose is to supply the high frequency PWM pulse peak MOSFET switching currents. Battery DC input PWM rate runs from about 6 kHz to over 25 kHz. Low freq inverter, heavy transformers generally use lower PWM freq, while high frequency inverters run higher PWM switching freq. Below 15-20 KHz there is possibility of audible noise emitted as this is within human hearing range.
It is not only the capacitance that is important but also the ESR (effective series resistance) of the capacitors. Also, parasitic circuit inductance is important.
Peak high frequency pulse current can be 4 to 6 times the average DC battery current. Even at high frequency this still takes a respectable amount of capacitance to supply the peak high frequency current pulse of hundreds of amps over the period of the high freq pulse. You typically find three or four 5,000 to 10,000 uFd electrolytic caps in parallel for these input capacitors on inverter PCB.
Insufficient or degraded input capacitance causes large voltage ringing spikes in conjunction with series inductance of battery cables. The voltage ringing can damage components in inverter, particularly switching MOSFET's due to exceeding their breakdown voltage rating. It is advisable that positive and negative battery cables are taped together. This reduces battery cable series inductance by better than half the value thereby reducing voltage ringing on inverter input compared to pos and neg cables run with 6-12 inches of separation. Taping pos-neg battery cables together also helps to cancel their nearby magnetic fields that can cause 120 Hz buzz in nearby metal objects, like a metal breaker box.
Contrary to common mis-perception, these input capacitors do very little to nothing to reduce the large 120 Hz ripple current on battery lines for a sinewave inverter. That would take many Farads of capacitance in accordance with I = C * delta V / delta time, where time is the gap between 120 Hz peaks. The peak 120 Hz ripple current is a bit greater than twice the average DC battery current and can be greater for poor AC power factor loads like inductive AC motors.
There is another somewhat mis-perception on making initial battery input connection to inverter which results in high surge current to charge these caps to battery voltage. Any reasonable quality cap is capable of taking this surge current with all the series resistance in battery, BMS, battery cables, and inverter PCB connections. Some cheap BMS's may trip for overcurrent although most have sequencing of the parallel current pass MOSFET's to limit startup surge current or an additional separate MOSFET with series power resistor to limit initial surge current.. The most damaging effect is that of pitting expensive high current DC breaker contacts which over multiple make/breaks increases the breaker resistance so breaker gets hot during high load current and potentially burning up.
This is related to a point that is often discussed on this forum. A lot of people are concerned that when a BMS first turns on, the surge current will be a problem that could either cause the BMS to think there is a short and turn back off or, worse, damage something. However, I don't see this in real life.....and I don't hear reports of this actually happening on the forum.Yes, a single mosfet can charge a very large bus without a resistor if it is turned on in a particular manner. I wonder what the BMS I a putting into my system is using for start-up. Good points - thanks.
This is related to a point that is often discussed on this forum. A lot of people are concerned that when a BMS first turns on, the surge current will be a problem that could either cause the BMS to think there is a short and turn back off or, worse, damage something. However, I don't see this in real life.....and I don't hear reports of this actually happening on the forum.
Good news. I threw this around last week and you replied. I'm going to omit the precharge circuit unless I find out I need it. I decided on a 200A Class T. It should be able to get the bus up to 60v without getting close to the melting I^2t. I picked out a beaker with a type D curve that likewise should not be bothered by inrush.
Yes, I would still do a pre-charge circuit on any inverter disconnect switch...... but that appears to be a different case than when the BMS is turning on and off. From experience, it appears that when the BMS turns on, the FET current ramps slow enough to avoid problems. Whether this is a happy coincidence or by design, I don't know.That may depend on how much capacitance your inverters have, and battery internal resistance.
Class T fast acting or slow blow?
Do I need a fast acting or slow blow fuse for Growatt 6kW inverter? I'm looking at about 125A I have used Class T fast acting fuses in industrial inverters. These inverters have resistor/relay charge limiting circuits though. Those damn fuseholders are expensive :(diysolarforum.com
My Push Button Pre-Charger Install for the SW 4024 Inverter
That kind of inrush might not harm the inverter, but it might blow fuses. class-t fuses @ $40 a piece make a $20 precharge circuit worth it. Ehhh. I dunno. I think class-t fuses are usually pretty fast, but the inrush we are talking about is a small fraction of a second. I'm not convinced it...diysolarforum.com
I was just thinking there really isn't a rule of thumb or a clear cut formula . When running 3 phase motor drives off of grid there is quite a bit of 360Hz ripple. If there is line imbalance we see 120Hz as well. Both the fundamental output frequencies and the carrier rates each produce another set of bus currents. With (60Hz) inverter running off batteries there will be a 120Hz component. I expect these 120Hz products might best be dealt with electrolytics, while film /ceramic might be best for the higher frequency currents produced at the carrier rates.I am curious: Why do you ask?
I would want the high frequency taken care of at the bus structure.. It never gets a chance to travel down the battery cables. i think covering the available area with a mix of different technologies would be best. I like ceramic right there. I suppose the best design would put a lithium battery pack very close to the bus. Some kind of current sensor between them. Yea, battery is good for supplying ripple current - a lot like a capacitorMy scope measurements of battery ripple show a substantial portion of the 60 Hz current comes from battery. I only ran the inverter at 40% load, but think if it was 100% load nearly all ripple current would come from the batteries. Battery is pretty "stiff", so not much voltage ripple allowed, therefore not much power supplied by caps.
I think even the electrolytics mostly supply higher switching frequencies to a LF inverter.
For a typical HF inverter, the electrolytics would probably supply the 60 Hz, but with much higher voltage ripple.