It limits the power from the AC source and calls upon the battery to assist powering the loads.What the hell is peak shaving?
Is that akin to gen assist on a Victron Multiplus?
It limits the power from the AC source and calls upon the battery to assist powering the loads.
Correct, but I suspect Sol-Ark just deleted the selection from the GUI, not the functionality. Sol-Ark tech support told me to wait and see if the selection is available in the new MySolArk monitoring app that should be available in May.So in the absence of CTs and gen peak shaving this is the only option on the solark settings.
In the current setup, the generator supplies the house first then the batteries. In the event 2 large loads kick in (dryer running and AC or stove) the generator will trip as it can't supply the load. But the batteries can. I have a Honda EU7000is inverter and a Generac XT8000e. The generac can supply multiple loads but again its more about the fact that it feeds the house rather than just the batteries.So op, are you worried about overloading the Gen because you are charging and supplying loads at the same time or does your base load exceed what your generator can supply?
I guess that's where I'm not clear
Have you tried setting the Gen Limit power to something like 80% of the Generator? When a surge happens, there may be enough headroom for the generator to surge, and not exceed its capacity before the Sol-Ark can switch from Charging to Supplying Power.
Otherwise, get a Chargeverter and charge the batteries directly.
This is the functionality that Sol-Ark says they no longer support. If loads + charger exceeds the Gen Limit setting the inverter will curtail charging, it will not reverse and help power the loads.Sol-Ark can switch from Charging to Supplying Power.
Yes, but I would try it anyway.This is the functionality that Sol-Ark says they no longer support.
Put large loads on a sub-panel. When running off generator, turn off the sub-panel. If you want to run something off the sub-panel, turn off the generator, and then turn on the sub-panel.In the current setup, the generator supplies the house first then the batteries. In the event 2 large loads kick in (dryer running and AC or stove) the generator will trip as it can't supply the load.
They may have taken it away from the gen port but it's apparently still available on the grid port, so can you connect your gen to that?In the current setup, the generator supplies the house first then the batteries. In the event 2 large loads kick in (dryer running and AC or stove) the generator will trip as it can't supply the load. But the batteries can. I have a Honda EU7000is inverter and a Generac XT8000e. The generac can supply multiple loads but again its more about the fact that it feeds the house rather than just the batteries.
Seems like others have said the capability used to exist but not so much now.