If it's that cold, how much sunshine is actually available?
Quite a bit actually. Cold winters tend to have a lot of sun. Think of places like Alaska etc.
how is it very very low, but still above BMS trigger point? Isn't this a contradiction?
A guy from this post would beg to differ. Such approach creates false sense of security and often leads to completely destroyed battery. Not saying it's not possible to manage it your way, but it seems to me that an actual good BMS that does not need bypassing would be a simpler and more reliable solution regardless of how the battery is used.Not at all. One BMS might cut off all discharge at 2.2v, another at 2.6v, another at 2.8v, and others might not shut off at all at the cell level. If I only want to cycle my battery down to say 3.1v, those BMS's would be useless to stop a single cell from going much lower. And if running an inverter straight from the battery, bypassing the BMS (which is common here), the BMS won't do squat to protect the one low cell. Any way you look at it, a battery that frequently is drawn down to low levels is probably safer with a bottom balance.
Those hypothetical "BMSs" you described above cannot be called a "good BMS", so how does it help any argument? Just don't buy crappy BMS, get a good one that fits your application. BMS must be able to disconnect the battery before any one cell goes outside of safe range. If a BMS does not meet this simple description, then it's not a real BMS, so you don't need to work around it, just don't buy it in the first place.
With all that said, I totally agree with you on small LiPo packs used in RC world. This application is better off without a BMS onboard, just set conservative limits on your ESC and only use BMS integrated in the charger to prevent overcharge. If your expensive plane or chopper or drone is at stake, sacrificing a battery is a much better choice than crashing into the ground.
I also have a rule of thumb, if BMS costs more than 20% of your battery cost, consider a simpler BMS or a larger battery.
Exactly my point. But the discussion rocks.I'm not sure if that's a good thing or a bad thing...
"he was among the first to emphasize scientific accuracy in his fiction, and was thus a pioneer of the subgenre of hard science fiction. "
Regardless of top or bottom balance your usable battery capacity is limited by the smallest/weakest cell. Whichever balance strategy is used, you still line up your charge and discharge by the bookends of the weakest cell, so how am I leaving anything on the table? My argument against bottom balance is that people still attach a BMS to the battery and most commercial BMSs are top balancing, so from day one your BMS will work against your initial bottom balance, making it useless. Bottom balance is only good when you run without a BMS, even though you are likely to kill your smallest cell by being oblivious to its voltage shoot at the end of charge, assuming that by lowering your charge target you somehow protected the first cell from grossly overshooting at the top. Even new cells come with 1-2AH spread, which is enough to damage the smallest cell while others are barely reaching the upper knee.Even with the perfect BMS, why, in the scenarios I describe, would you want your cells balanced at the top rather than the bottom? You'd be leaving a lot of capacity on the table if top balanced older batteries are used, and it will get worse and worse until they are bottom balanced.
You don't charge to 3.4V, it is not practical, you'd be wasting most of your battery investment.
Can't speak for everyone, but I personally don't comment on "WHAT IF" posts describing something that is not a real thing or something that never happens in practical applications. Life is too short to engage in useless pondering.
Do you have a source I can look into? I have analyzed Tesla BMS boards taken from a wrecked car and did not see any evidence of active balancing. All I saw is a classic top balance scheme with tiny amount of balancing, which is all you really need when using top quality perfectly matched cells.Tesla uses this approach.
How can you tell you are stopping at 90%? Does your charger know the SOC of your smallest cell? How can you set your charger's pack voltage precisely matching your weakest cell's voltage corresponding to it's 90% SOC? You'd have to experiment by carefully monitoring end of charge and stopping when your smallest cell reached the desired voltage, then recording the pack voltage at that moment and setting your charger to that level, so next 1000 charge cycles will end precisely the same level relative to that particular cell? This implies you even have a charger where you can control the target voltage with such precision, if at all. Not many chargers out there with flexible voltage settings.Instead, we just oversize the pack a little bit and live simply by stopping at 90%.
Yes, you can. But I can't as I value time more. The best quality of LFP is ability to accept fast charge, I don't want to give it up. I design all my batteries to be able to charge fast, so people can take advantage of short solar hours or engine runs, reduce generator runtime, etc. Everyone wants a fast charge. This is why I said not practical, but not impossible.You can slowly charge LFP to 96 or 97% SOC at 3.40Vpc
Think about it, active balance schemes are all based on reducing voltage differential, as if that is the goal. When battery is actively used, voltage differential can be perfectly normal due to spread in IR between adjacent cells. Voltage differential does not mean difference in SOC, so if you are trying to equalize voltage, you are actually hurting the SOC balance, which should be your real goal. As such true SOC balance, either top or bottom, can only be achieved at the vertical knees of the curve, where relationship between SOC and voltage is known. Anywhere in between this relationship is moot and so you can't use voltage as a measuring stick.
Yes, all of this can be done, but why bother with all this complexity when you can just slap on a decent BMS, pick any decent charger, even if you can't tweak it's voltage, and move on to the next project without ever worrying about any drift or imbalance.
I don't mean to sound like I'm quibbling with your terminology. But I have lived full time off of my battery for 2.5 years now, and I have a lot of incentive to charge fast, to not run my generator longer than I need to, and to harvest all the solar I can get. And those desires are not incompatible with a conservative CV threshold.
Here is a very typical graph from a recent charge. This charge began at about 55% SOC and delivered energy at about 0.16C:
You can see the charger was in CC until about 7pm, after about 2.5h. The labels show that about 18.4kWh was shoveled into the battery in total. For the last 45 minutes of CV, the total energy delivered there was about 2.5kWh, or 13% of the total but using 25% of the time. That last bit of charging was only 50% as time-efficient.
So, yeah, that kinda sucks? Except:
(a) I could always just decide to stop at the CV threshold and skip that last sliver if I really hated listening to the genset. That "wasted" bit is only 6% of pack capacity.
(b) Even with a BMS and a top-balance, one still hits a CV regime -- and the higher the rate, the earlier. As soon as the charger shifts into CV, the characteristic curve should look similar to the one above... and thus, there is "waste."
(c) In many scenarios, I have unlimited low-level charging available. That occurs when on shore power, or on sunny days when there is excess PV. In those cases, the very small CV portion is not wasted, because there is no opportunity cost for that energy.
I respectfully submit that conservative stop-charging voltages and a slightly-oversized pack can produce a pretty darn good, practical, workable result. I'm right here living in proof of it!
Are you running solar for you home, RV, work?? Just curious -- your knowledge is outstanding and the way you explain things is really understandable ...
@nebster my hat is off to you, you did a wonderful job of a highly specific and customized system that perfectly fits your needs. But you cannot argue that it's practical for most DIY projects?
I bet you have at least some EE education and experience to pull this off.
I am ranting on forums because I see plenty of Youtube videos and forum posts where people follow some half baked advice to bottom balance their cells and then proceed to charge them at a max pack voltage, oblivious to some cells shooting thru 4V and beyond, because they never even monitor on cell level, and then after a while when the pack is damaged they blame getting used cells or Chinese conspiracy, etc.
Also, you have a 16S battery, so tweaking charge voltage is easier. Much harder on most common 12V systems, especially when alternators are used for charging, which are terrible at voltage regulation.
I'm curious why many parallel strings? Is it due to physical space layout? Or you don't trust parallel cells in a single series string?
From my experience, I prefer to charge to 3.5V-3.55V to get a good trade-off of fast enough charge, yet still plenty of charge cycles. Calendar aging and temperature will do them in before cycle life anyway. Oversize AH as much as reasonably possible to reduce average DOD. Not a fan of bottom balance because I always use a BMS and find top balancing just so much easier to do.
Thanks for sharing your project, much appreciated. Sorry I can't share much of mine due to NDAs.
I do have a 10kWh home battery setup in a fully automated peak shaving cycle, shifting 10kWh every day from night hours to peak day hours. Has been cycling for a year now, more than 3 MWh time shifted by now. Used CALB cells rescued from previous EV application. Cells are 5 years old, 4 years in EV and one year in daily 90% DOD cycle, still running strong at about 90% of original sticker rating.