Hello all,

I have seem to have gone down the rabbit hole trying to figure this out. I have a PSW-H 3kW 120Vac 24V Phocos inverter. The inverter has relay contacts that of course will turn the generator on when the batteries reach a certain voltage and off when they reach a certain voltage. I am having a heck of a time figuring out how one would go about wiring these relay contacts to a generator that would serve this purpose. Any insight into this would be greatly appreciated. I'm not looking for any particular model gensets, or rated power, I'm looking for more of a general idea of how you would pair these two. I know other inverters have these same type or relay contacts but I can't seem to get a straight answer.

Thank you so to anyone that can help me out with this.
 
Here goes my $0.02
The C = common so you would connect your hot wire or feed leg to it.
NC = normally closed so this contact will be hot until relay coil is is powered.
NO= normally open. Contact is open or off position until relay is powered and pulls contacts closed.

Depending on how your relay is connected to in your inverter as to which contact you use. Conect your supply leg that will start your generator to the common (C) and see which other contact is hot when batteries are fully charged.

You will then want to connect the return our start wire to the contact that is not hot when batteries are full. As it will be the one that the relay switches to when generator power is needed.
 
For automatic generator starting, there are basically two different control components.
1) The signal that says "I Need you to start" to the generator. This is done with a set of relay contacts that sent the appropriate AC or DC current, or just close to tell the generator to start.


2) The Automatic Starting system for the generator. This is a unit that closes the relay between the starter motor and the battery, it then keeps this relay closed for a set amount of time and then senses if the generator has started. Different starters have different options. Some have settings for how long to crank the engine, others have settings for how many attempts to make, and others have different "Is the engine running?" sensors.
For any generator that is auto start from the factory, it should just be a matter of running two wires.. When a relay makes contact between the wires, the generator starts.. when the contact breaks, the generator stops.


Generator Auto Start is probably NEVER going to be included with any inverter.. that module will be part of the generator itself, or an add-on component you can purchase separately. Google "Automatic Generator Starter".. They're pretty cheap at only around $100 to $200 for a basic unit.
 
Here goes my $0.02
The C = common so you would connect your hot wire or feed leg to it.
NC = normally closed so this contact will be hot until relay coil is is powered.
NO= normally open. Contact is open or off position until relay is powered and pulls contacts closed.

Depending on how your relay is connected to in your inverter as to which contact you use. Conect your supply leg that will start your generator to the common (C) and see which other contact is hot when batteries are fully charged.

You will then want to connect the return our start wire to the contact that is not hot when batteries are full. As it will be the one that the relay switches to when generator power is needed.
Thank you so much for the response, I deeply appreciate it ?
 
For automatic generator starting, there are basically two different control components.
1) The signal that says "I Need you to start" to the generator. This is done with a set of relay contacts that sent the appropriate AC or DC current, or just close to tell the generator to start.


2) The Automatic Starting system for the generator. This is a unit that closes the relay between the starter motor and the battery, it then keeps this relay closed for a set amount of time and then senses if the generator has started. Different starters have different options. Some have settings for how long to crank the engine, others have settings for how many attempts to make, and others have different "Is the engine running?" sensors.
For any generator that is auto start from the factory, it should just be a matter of running two wires.. When a relay makes contact between the wires, the generator starts.. when the contact breaks, the generator stops.


Generator Auto Start is probably NEVER going to be included with any inverter.. that module will be part of the generator itself, or an add-on component you can purchase separately. Google "Automatic Generator Starter".. They're pretty cheap at only around $100 to $200 for a basic unit.
This is the answer I was searching for. Thank you so much for taking the time to explain this.
 