The nominal battery pack voltage in my system, which is 128S 3.4V LFP cells or (8) 51.2V batteries is series is 409.6V nominal in 3 strings, each string as its own circuit breaker and a combined voltage / current meter so I can watch current sharing for charging ( its so far dam near perfect ) likely due to the low current involved, so the voltage drop is not an issue that 49V systems has. I charge at 10 amps ( 4kW ) which is only 20% of the inverter rating, system is whole home backup only and I'm grid tie with 15kW solar.
2 of the 3 stings are
50Ah each ( 100Ah total ) and after the circuit breaker(s) is parallel with the BYD batterybox HV ( 10 kWh ) which has canbus closed loop with the slave S6.
The 3rd is 30Ah parallel after the circuit breaker with the
Seplos Hitens ( which are parallel each 20kWh) and is closed loop with the master S6, technically 55Ah total
The primary concern / issue with series battery's is when one battery in the string discharge mosfets in a generic BMS goes offline you can have very large voltage across the offline battery as the positive of the total string will go to ground from the inverter battery positive, could be up to negative 3XX volts which would have the BMS FETS blow up. ( single series string )
So when a "dumb" string is paralleled with a string with communications, it is protected as the two possible cases are:
- Communicating battery goes offline, inverter shuts down the battery port, naked battery safe
- No communications battery goes offline, communicating battery maintains the string pack voltage so no large voltage differentials on an individual battery.
Wire size:
Since this is HV, the
S6 has a maximum continuous rated battery current of 50 amps and the pack voltage is ~409V is well above the inverter rating of 11,400 watts. And at 11.4kw that's only a draw of ~28 amps , so 10 awg is fine for the battery and that is actually less as that is split between 3 battery's, less than 10 amps each at full rated load.
One can use lower pack voltages, but you need ~230 as a minimum @ 50A for the 11.4kW rating and just keep in each battery cell count an even divisor of the total pack voltage of the battery with closed communications to the inverter of the parallel pack voltages are the same.
As for concerns about current sharing the parallel packs, uneven discharge will rotate from pack to pack as the charge or discharge ( ohms law ), but be close enough for bottom and top SOC anything in-between is unknown and doesn't have any functional value as one has no control even if all batteries were perfect in reporting SOC.
The down side of this is this system isn't UL9540 ( BYD and
S6's are is but nothing else )
Works great, fun project to build and keep me busy, your mileage will vary if you should choose this path.