Low frequency inverters are always single inverters.I guess what I’m confused about is that the 6048 is often described as 2-3k units in one box to create split phase.
I’ve also seen it described as LF
Is the 10k y&h/srne the same in that it would be 2-5k units in one box to create a 10k split phase inverter
Which leads to, is that then also how the Growatt 12k is designed?
Or is another way to phrase it, are all LF split phase inverters just two smaller inverters in one box?
In your reply you said “full rated output from each at 120 or together at 240” so in the case of the 6048 would that mean that when people gripe about “load imbalance” is that one leg may have multiple larger 120v items running and the other leg does not, thus creating the imbalance? And then would unbalance not technically be the correct word as there’s really only 3k available to that leg, If so, is that simply a matter of which 120v circuits are connected to which leg? And then with 240 appliances the imbalance issue is irrelevant because it’s pulling from both legs?
Am I understanding this properly?
If so, what then happens with 2 or 3 split phase units in parallel. Does that create more or less imbalance risk
High frequency split-phase inverters are always two inverters. Either in one enclosure or separate enclosues.
Low frequency means that they use a transformer.
Inverters have their limits. Transformers have their limits. To save costs, both can be value designed. And sometimes rely on each other to boost output.
But rated output is based on all of the individual parts.
The best option for balance is two inverters. Whether high or low frequency. Or a fully rated external transformer.