Alright, Black Friday got the best of me:
Fronius Primo 10.0-1 Inverter
Fronius Quattro Rapid ShutDown
Kinetic Racking & Hardware
12.7 kw Jinko 455 watt bifacials(28)
300' of both Black & Red PV wire,
Time to Grid Tie! My electrician has never done a grid-tie before, and I have a good enough relationship with him to opt in and be the guinnea pig. We're adhering to 2018 Electrical Code in New Brunswick.
I'm going to be building a rather large "pergola," so that's definitely what needs to happen first. The rapid Shutdown come with the "kit" so I may as well make use of it, even though I'm sitll not sure if a pergola is considered roof, or ground mount really. Figured this would cover me either way. But, this brings a problem. Primo can handle 1000vdc, so 2 strings of 14 would have been perfect.
However, Quattro can only handle 600vdc, so I have to change my setup a bit. 2 strings of 9 panels brought together at a combiner, then another string of 10 going straight into the quattro. Figured it was the best way to keep my voltage up enough.
I think it's best to have the Quattro close to the array, run the 2 wire contact to the inverter in the same duct as the 2 PV strings coming in (3 strings going into the Quattro, 2 exiting), maybe in a 2" PVC? I'm not up on ducting requirements, will confirm with electrician.
Now, where Quattro Rapid Shutdown brings PV voltage down to 30v, does this negate the need for a DC Disconnect entirely? I get that it's still live after being activated, just didn't know if it was redundant to do so. I also get that it's acting like my combiner box as well, so that's one thing going for me.
Also, PV wire coming in around 450Voc, should that be metal clad once it enters the home? I'm working on One-Line Diagram now, kind of want to understand this as much as possible before submitting. I have a Powerline Technician background, so electrician stuff i'm really relying on my electrician helper. I don't want to bug him with 1000 questions, especially on something he's never taken on before. Small Island, not a lot of people, make the best of it kinda thing.
Any help is greatly appreciated! I will post one line diagram so it can be critiqued/laughed at before sending to utility. I really do encourage laughter.
Fronius Primo 10.0-1 Inverter
Fronius Quattro Rapid ShutDown
Kinetic Racking & Hardware
12.7 kw Jinko 455 watt bifacials(28)
300' of both Black & Red PV wire,
Time to Grid Tie! My electrician has never done a grid-tie before, and I have a good enough relationship with him to opt in and be the guinnea pig. We're adhering to 2018 Electrical Code in New Brunswick.
I'm going to be building a rather large "pergola," so that's definitely what needs to happen first. The rapid Shutdown come with the "kit" so I may as well make use of it, even though I'm sitll not sure if a pergola is considered roof, or ground mount really. Figured this would cover me either way. But, this brings a problem. Primo can handle 1000vdc, so 2 strings of 14 would have been perfect.
However, Quattro can only handle 600vdc, so I have to change my setup a bit. 2 strings of 9 panels brought together at a combiner, then another string of 10 going straight into the quattro. Figured it was the best way to keep my voltage up enough.
I think it's best to have the Quattro close to the array, run the 2 wire contact to the inverter in the same duct as the 2 PV strings coming in (3 strings going into the Quattro, 2 exiting), maybe in a 2" PVC? I'm not up on ducting requirements, will confirm with electrician.
Now, where Quattro Rapid Shutdown brings PV voltage down to 30v, does this negate the need for a DC Disconnect entirely? I get that it's still live after being activated, just didn't know if it was redundant to do so. I also get that it's acting like my combiner box as well, so that's one thing going for me.
Also, PV wire coming in around 450Voc, should that be metal clad once it enters the home? I'm working on One-Line Diagram now, kind of want to understand this as much as possible before submitting. I have a Powerline Technician background, so electrician stuff i'm really relying on my electrician helper. I don't want to bug him with 1000 questions, especially on something he's never taken on before. Small Island, not a lot of people, make the best of it kinda thing.
Any help is greatly appreciated! I will post one line diagram so it can be critiqued/laughed at before sending to utility. I really do encourage laughter.