all the clones doI have an MPP hybrid-inverter, and SunGold's manual looks just like MPP's
I repeated wattmatters search. I even used NordVPN to set my location to Australia. I had hope that SunGoldPower website would link me to Australia, but no back to USA. My search results were the same as wattmatters.Who is their local support in Australia? Never heard of them. Website mentions nothing other than they've sold to customers here but no mention of local support. None of their inverters are suitable/designed for our electrical system.
They look like a clone manufacturer.
That sounds like a good plan. I don't think any hybrid is going to AC couple very successfully without batteries or a fairly consistent load. In the meantime, until you get batteries, you could just switch off some of your GT inverters when you do have a power outage and you want to use some solar. The more consistent loads you have in that scenerio the less buffering the grid forming inverter has to do as loads change. The batteries do the buffering that the grid typically does when the grid is up. The SolArk does use the generator port so it can quickly disconnect the AC coupled GT inverters if frequency Watt cannot get them to ramp down quickly enough/It seems that my best option is to use the new 15KW Sol-Ark hybrid inverter ($8K), since it can be installed without any batteries and AC couple my existing 15 KW Fronius grid-tie inverters.
Just regular cost. You get what you pay for..Besides Schneider/Outback/SolArk/SMA (high cost), which hybrid/all-in-one can even turn on GT ? let alone AC coupling ?
Fronius are grid following inverters. They can be controlled by a grid forming inverters using AC frequency control.I am curious to find out if the Fronius can be AC-coupled.
Excellent question that I need to ask before buying the new Sol-Ark 15 KW SA-Limitless hybrid inverter. Modulating the 15 KW grid-tie inverters output is only needed when the grid is down, because I need to maximize the grid-tie inverters output when the grid is up and store about 2/3 of production on the grid to be use later.Fronius are grid following inverters. They can be controlled by a grid forming inverters using AC frequency control.
This is how they work with Tesla Powerwall 2's inverter when operating in grid outage mode, and micro-grid forming inverters such as the Selectronic can take control of a Fronius, adjusting the micro-grid frequency so as to control the output from the Fronius.
As with all such things, it requires careful design - there is a limit on the size of inverter capacity which can be controlled in this manner - it shouldn't be greater than the ability of the off/micro-grid system's capacity to manage a dump load, e.g. the instant should the grid goes offline while the grid tied PV system is cranking out full power under the Summer sun.
Fronius are grid following inverters. They can be controlled by a grid forming inverters using AC frequency control.
This is how they work with Tesla Powerwall 2's inverter when operating in grid outage mode, and micro-grid forming inverters such as the Selectronic can take control of a Fronius, adjusting the micro-grid frequency so as to control the output from the Fronius.
As with all such things, it requires careful design - there is a limit on the size of inverter capacity which can be controlled in this manner - it shouldn't be greater than the ability of the off/micro-grid system's capacity to manage a dump load, e.g. the instant should the grid goes offline while the grid tied PV system is cranking out full power under the Summer sun.
SunGoldPower IP6048 are UL 1741 listed and listed as AC coupling hybrid inverter. My problem is they require a 40 amp breaker between the inverter and the grid and the description was clear that the grid-tie inverters can feed the batteries when the grid is down. I would assume that if I'm only trying to send 15 KW to the grid, which is about 65 amps that two of these hybrid inverters in parallel might work assuming 80% breaker capacity. As an engineer, I would want (3) inverters as a minimum. I could buy (2) Blue Power IP6048 with (4) 5 KWH SOK batteries now and in a few month add another inverter with (2) 5KWH SOK batteries. The initial cost is either $8K for Sol-Ark or $12K for SunPower. Total cost for both systems is about $18K plus shipping, miscellaneous parts and installation. My gut feeling is that, if I going to spend $12K that the better solution is Sol-Ark with (2) 5 KWH SOK batteries.I am curious to find out if the Fronius can be AC-coupled. Heard in the past that it's difficult with Fronius GT.
~$20K is too pricey for me
here's MPP email response to my inquiry about Sungold: " Sungold power is one of our OEM brands. . a company owned by the Chinese and has a company also in the US."
I am doubtful whether these cheapies can do grid-tie function, and surely not "approved"
Excellent question that I need to ask before buying the new Sol-Ark 15 KW SA-Limitless hybrid inverter. Modulating the 15 KW grid-tie inverters output is only needed when the grid is down, because I need to maximize the grid-tie inverters output when the grid is up and store about 2/3 of production on the grid to be use later.
After reading your quote, I'm thinking that maybe my best option is to replace one of the 5 KW Fronius Primo inverter with the new Sol-Ark 15 KW hybrid inverter. It seem like it would be simpler to swap an existing Fronius inverter for a the new Sol-Ark hybrid inverter versus doing a complete new inverter installation.As an example, for Powerwall 2 installations in Australia, when set up to operate in grid outage mode and take control of the GT inverter, the GT inverter cannot have an output capacity greater than 7 kW. That's because the Powerwall has a max surge absorption capacity of 7 kW, which buys it enough time to get the GT inverter's output under control. It cannot be coupled with a GT inverter with higher rated output.
If the battery it at/near full, then the PW's inverter will immediate raise the micro-grid frequency to about 5-6Hz above the regular grid signal frequency, and that's sufficient to shut down the GT inverter temporarily. As the Powerwall's battery is discharged its inverter begins to reduce the frequency of the micro-grid and eventually the GT inverter will start to operate and generate output, but throttled according to how far above the standard frequency the grid signal is.
Hence for homes with larger solar PV systems, Tesla advise having more than one GT inverter, and having the Powerwall control one inverter, typically a 5 kW unit with up to 6.66 kW of PV but you could have a 6 kW inverter. This keeps it nicely within the spec of the Powerwall's capacity to manage a dump load.
That means only that one inverter and its PV array remain online during grid outages but for essential load support during grid outages it's usually enough to keep things running (normally the system is set to supply power to selected circuits only during outages). The rest of the GT PV system remains off-line. You can of course add more batteries to enable the rest of the PV system to also operate.
To justify my actions, I do have 5 electrical panels plus the panel for the inverters. Usually a critical load panel is installed next to the house panel and you simply move circuits to the new critical load. Simple task for most, but not for someone with 5 electrical panels that are scattered all over the house. The Sol-Ark Limitless 15 KW hybrid inverter is advertised with an AC couple solution. However, I'm anxious to buy, but want to do my due diligence and make that it will work with the (3) 5 KW grid-tie Fronius inverters. Hopefully, if I substitute the Sol-Ark hybrid inverter for one of the GT inverter, I then have 6 KW of solar panels that will normally satisfy the load most of the time and only need AC couple to control the remaining two GT inverters.trying to AC coupling a 15kw system is a very tall order, while it may seem convenient to avoid having a separate critical load panel; but a hefty transfer switch is also needed upon islanding. The other design parameter to consider is how often and how long are the outages ? which are different for different local region.
Replacing one of the Fronius inverters sounds like a good plan for the reasons you articulated. The easiest way to determine if the remaining Fronius can be controlled by the SolArk is to see if they comply with UL1741?Any suggestions???
I just check the original Fronius proposal from 3 years ago to make sure that the Fronius installed were UL1741.Replacing one of the Fronius inverters sounds like a good plan for the reasons you articulated. The easiest way to determine if the remaining Fronius can be controlled by the SolArk is to see if they comply with UL1741?
That should work. It will respond to frequency Watt by going off line then come back if the load is increased. Only the newer 1741SA will modulate but that is another reason to put panels on the new hybrid. DC coupled panels on a hybrid respond faster and will modulate. That will be a good balance of functionality.The Fronius Data sheet included with the proposal shows "Certificates and compliance with standards: UL1741-2015,
Thanks for sharing your knowledge on UL1741 and UL1741SA. It is really helpful and encouraging that my existing (3) Fronius Primo 5 KW GT inverters can interface with a new hybrid inverter. Hopefully, I'm evolving and becoming more knowledgeable thanks to the DIY Forum.That should work. It will respond to frequency Watt by going off line then come back if the load is increased. Only the newer 1741SA will modulate but that is another reason to put panels on the new hybrid. DC coupled panels on a hybrid respond faster and will modulate. That will be a good balance of functionality.