Hey everyone!
My wife and I decided to get solar installed on our primary home finally, and we decided that it wasn't worth the time and effort for me to do the work myself, since it would involve climbing up on a 14/12 pitch roof (NO THANK YOU) to do the install work.
Anyway, long story short - I found a reputable solar installation company and signed a contract for them to do the work.
I decided to get a solark 15k inverter, and 45 panels (460w) - here is the datasheet.
The company sent me their engineering plans, and for some reason, their engineer thinks that the solark 15k cannot support all 45 panels. I'm 100% certain that their engineer is just plain wrong, and I'm arguing back and forth over email with them.
Can you kind folks please fact check me to make sure I'm not being an idiot somehow with this? Here is the email I sent them most recently, and I'm still waiting to hear back their reply. By the way, apparently they opened a support case with Solark to find out if I'm right?!? (which I'm really annoyed by, because isn't this literally the reason why I'm PAYING SOMEONE ELSE TO DO THIS FOR ME?!). I'm super frustrated right now tbh. Anyway, here's the email:
My wife and I decided to get solar installed on our primary home finally, and we decided that it wasn't worth the time and effort for me to do the work myself, since it would involve climbing up on a 14/12 pitch roof (NO THANK YOU) to do the install work.
Anyway, long story short - I found a reputable solar installation company and signed a contract for them to do the work.
I decided to get a solark 15k inverter, and 45 panels (460w) - here is the datasheet.
The company sent me their engineering plans, and for some reason, their engineer thinks that the solark 15k cannot support all 45 panels. I'm 100% certain that their engineer is just plain wrong, and I'm arguing back and forth over email with them.
Can you kind folks please fact check me to make sure I'm not being an idiot somehow with this? Here is the email I sent them most recently, and I'm still waiting to hear back their reply. By the way, apparently they opened a support case with Solark to find out if I'm right?!? (which I'm really annoyed by, because isn't this literally the reason why I'm PAYING SOMEONE ELSE TO DO THIS FOR ME?!). I'm super frustrated right now tbh. Anyway, here's the email:
Let me clarify what I'm saying, since I'm not sure this is coming through clearly.
There are a few main and important points:
1. You CAN over-amperage MPPT inputs safely. There is no damage if you have too many amps going into MPPT inputs, the inverter will just self-limit the incoming wattage to its theoretical max of 6.5kw per MPPT.
Per the solark 15k manual:
"Max DC solar input = 19.5 kW (± 5%) | Max input power per MPPT = 6.5 kW | Max recommended input voltage per MPPT = 425 VOC, Max input current per MPPT = 26A (self-limiting)."
2. You CANNOT over-voltage MPPT inputs, it will fry the electronics.
3. When you put panels in series, it increases the voltage, and when you put panels in parallel, it increases the amperage.
So the solark 15k has 3 separate MPPTs, where each one can support a max (+/-5%) of 26 amps (6,500w), and as long as the power stays below 44a per MPPT, it can self limit the power safely.
5 panels in series would mean a max VOC well within the 500v limit. Then you would parallel 5 and 5 more panels to increase the amperage of those panels. This would be a single string of 5x3 panels, for a total of 15 panels per string.
The max power output of these 15 panels would be 6,900w, which is just barely above the max 6,500w input power per MPPT, but again, this is fine because the MPPT will self limit the power input.
The Solark can accept 6 total strings as inputs, but it's only THREE MPPTs in total. PV1 has 2 string inputs, and then the solark parallels them for you if you decide to configure it this way (which we wouldn't). From the solark manual:
This would be a similar configuration that I'm talking about, except we would have 5 panels in each "row" (series) with 3 rows (parallel), each using a Y connector to connect the rows together. In total this would be a single string.
Then we would do this 2 more times for the same total power output per MPPT.
Does this make more sense now?
Last edited: