From the manual:
Solar Charging Mode(Per number of MPPT) | |
INVERTER MODEL | 5KVA |
Rated Power | 4000 W x 2 |
Max. efficiency | 96% |
Max. PV Array Open Voltage | 145Vdc |
PV Array MPPT Voltage Range | 60~115Vdc |
Min. battery voltage for PV charge | 34Vdc |
I am assuming when hooking up PV to the PV input, Series sums the Voltage, and Parallel sums the Amperage.
I have two LV5048s (Left Picture). My plan is to do a 2S(maybe 3s) 4 times for each of the 4 PV inputs. I have 12 panels (right pic). I am planning to put at least 8 up this weekend, if the round2it's line up.
Can I do just one panel alone on each PV input? I see the 60~115VDC makes me think I have to have 2 or 3 in series of this panel.