I did not have any ferrules on my wire.The old ferrules strike again.
Throw those in the garbage and grab two Victron RS 450/100s. It's inevitable.I did not have any ferrules on my wire.
I believe the connector is the failure point or the wire internally is the problem.
The wires coming out the "top" (not your 4-AWG) that burnt and it's neighbour are seriously cooked, I'd say you got lucky !
I believe the failure is correctly identified in this post from the original thread. The termination is the fault.I'm assuming those two go up to the SCC Electronics ? What freakin gauge is that ? Looks like 10, maybe 8 ? me, shakes head in wonder, wth.
Panel ISC is 13.43A, IMP is 12.67AHow much current is through that? Seems like they underengineered something there.
Just the negative is cooked. In the original failure video I showed the internal wire gauge, it is 14AWG with 105C insulation.
I believe the failure is correctly identified in this post from the original thread. The termination is the fault.
I'm running JA Solar mono 530W panels, here are the specs:
I have 8S in a string, just one string on each MPPT. The EG4 MPPT is rated for 5500W and I'm only pushing 4240W into the MPPT. I have 10AWG THWN with 105C insulation on my side.
- Rated Maximum Power (Pmax): 530W
- Open Circuit Voltage (Voc): 49.65 V
- Maximum Power Voltage (Vmp): 41.84 V
- Short Circuit Current (Isc): 13.43 A
- Maximum Power Current (Imp): 12.67 A
Yes, checked every terminal including pulling the breaker and checking those on the other charge controller and this replacement at install.I can't remember after the last one did you check how tight the connector was when first installed? Is the one next to it still tight?
Really? The panels are somehow magically putting out more amps than rated? I have 8S and max ISC is 13.43AJust curious if you have put a clamp meter on it when it was operating to verify the current is what you expect? 14awg should be mor than enough, which would leave that connector they have as the real issue.
Not the right color for coordination.Throw those in the garbage and grab two Victron RS 450/100s. It's inevitable.
That's what I thought.Yes, checked every terminal including pulling the breaker and checking those on the other charge controller and this replacement at install.
I'm wondering if the connector is aluminum.That's what I thought.
An easy "fix" is to bypass like you said before to direct wire things, or install a different connector type, but you shouldn't have to do that. I wonder why they're loosening up, they aren't running loose and hot at first but something is clearly going on.
I'm wondering if the connector is aluminum.
Oh I agree with you, don't get me wrong.
But you have the equipment to just check it so I would. And I also agree with you and I would run the wire direct with 10awg now.
Maybe they are having this sort of failure a lot and just not saying anything. Or maybe you have just been unlucky. Just a bit odd it is exactly the same connector and wire as before.
And I assume by now you have already checked the other unit and found no issue? Wires not even warm.
Didn't no-ox or similar.Great point - did you put any no-ox or similar on the wires? shouldn't need to.
Do not take this wrong but although you checked the terminal for being tight did you also pull on the wire to ensure it would not easily pull out? Some of these darn blocks can allow you to insert a wire under the rising block and while it looks connected, and the screw is as tight as it can be, the wire sits without any hold on it.Really? The panels are somehow magically putting out more amps than rated? I have 8S and max ISC is 13.43A
The connector is faulty, if someone's house burns down they have a huge liability on their hands due to the connector. I don't know what EG4 will do about this problem but it will need to be addressed.
I don't know what pictures you're looking at or what evidence you are reading but everything I have seen here says that that 14 AWG is not up to the task.The 90c will do 15 amps, this is 105c - screen cap from the video so it will do closer to 20amps - he has 12.67 or should.