callmeburton
New Member
- Joined
- Mar 4, 2022
- Messages
- 347
I picked up a Outback radian box (empty) and a Outback Radian Load center off Craigslist earlier this year for $150 and planned on using it but didn't know where ...
Originally I thought the Outback Radian box had all the components in it but found out later it did not so I decided it would likely be a good candidate for my Eve 280ah 48vdc battery box ...
Currently I am wiring this up to be an always on microgrid within my current home that feeds all the circuits off our transferswitch. So the transfer switch would permanently be switched to "GEN" and be fed by the microgrid powered by the SMA SI off the battery bank. We are doing this as our new house we are building is 100% off grid and I wanted to use the batteries now and have the SMA and BMS preconfigured and ready to go and we get a lot of blackouts in winter.
https://diysolarforum.com/threads/sma-sunny-island-wiring-set-up.35605/post-657140 (post with the wire diagram for general top level connections between components) Diagram attachment here
The wiring for the batter to load center to SMA SI will be similar to my early mockup of my original Midnight solar setup I was originally planning to use. https://drive.google.com/file/d/1zBiWcO6m7j04EqA0LuignK4pw0Ez3b8m/view?usp=sharing (full res here, attached capture below)
I have a picture of the battery box conversion before I finished wiring up. I have foam on either side of the batter and backer board under and behind it. Batrium BMS sitting on outside. Even though this is "done" I still have not connected the sensor leads to the balancer and they continue to be connected to the tester just in case I mess something up while assembling it ... after I get a cover setup and secured I will migrate these connections from the tester to the blanacer.

The GS Loadcenter looked like it was configured for flex inverters to power the loads, or the grid to power the loads. The generator as wired wasn't connected to anything. And it appears the remote trip breaker could be powered by 12 or 48 volts.

I have now rewired it but I don't have a diagram to show the end results yet ... only that it closely matches the diagram above. I have the mechanical lockout breakers terminating at the AC2 output bar (which I drilled and placed top left in the image) and the inputs going from GEN or GRID. The remote circuit breakers relay for 12v has been removed and I retained the 48 volt relay and rewired it to hook up to the SMA SI or the BMS to act as a load shed relay. The input to the remote circuit is AC1 and the output goes to one of the other 50amp breaker for the LOADS. And this obviously goes to the loads buss bar.
The pre-charger cicuit sits top left and I connected the contactor directly to the DC breakers (which now have a pin in them so they move together) ... The red L2 buss bars have been removed and a din rail was placed in there for the Batrium BMS and expansion board ... I put 3 extra din rail fuse holders for that circuit bottom left near the existing din relay.
The neutral bar is no longer grounded, and the negative bus bar has been replaced with a short one and rotated to make it fit in the space I had as I had to replace the existing buss bar which was incompatible with the batrium shunt sensor. The following image doesn't show current state as I have everything wired up less the external sources (SMA COMM / Relay / inputs / outputs, Battery inputs / balancer) ... but this image is clearer as I haven't cleaned up wires yet since I need two more cables before continuing.

Will update this as I make progress. I am waiting for a shield cat 8 22awg cable to come so I can chop it up and use it as my coms cable to the SI and for the batrium balancer to the core unit (since it is also shielded)
EDIT: the breakers on this unit say 50 amp but if you flip them over or look at the side (wherever the label is) it says they trip at 63amp ... was happy to see that)
Originally I thought the Outback Radian box had all the components in it but found out later it did not so I decided it would likely be a good candidate for my Eve 280ah 48vdc battery box ...
Currently I am wiring this up to be an always on microgrid within my current home that feeds all the circuits off our transferswitch. So the transfer switch would permanently be switched to "GEN" and be fed by the microgrid powered by the SMA SI off the battery bank. We are doing this as our new house we are building is 100% off grid and I wanted to use the batteries now and have the SMA and BMS preconfigured and ready to go and we get a lot of blackouts in winter.
https://diysolarforum.com/threads/sma-sunny-island-wiring-set-up.35605/post-657140 (post with the wire diagram for general top level connections between components) Diagram attachment here
The wiring for the batter to load center to SMA SI will be similar to my early mockup of my original Midnight solar setup I was originally planning to use. https://drive.google.com/file/d/1zBiWcO6m7j04EqA0LuignK4pw0Ez3b8m/view?usp=sharing (full res here, attached capture below)

I have a picture of the battery box conversion before I finished wiring up. I have foam on either side of the batter and backer board under and behind it. Batrium BMS sitting on outside. Even though this is "done" I still have not connected the sensor leads to the balancer and they continue to be connected to the tester just in case I mess something up while assembling it ... after I get a cover setup and secured I will migrate these connections from the tester to the blanacer.

The GS Loadcenter looked like it was configured for flex inverters to power the loads, or the grid to power the loads. The generator as wired wasn't connected to anything. And it appears the remote trip breaker could be powered by 12 or 48 volts.

I have now rewired it but I don't have a diagram to show the end results yet ... only that it closely matches the diagram above. I have the mechanical lockout breakers terminating at the AC2 output bar (which I drilled and placed top left in the image) and the inputs going from GEN or GRID. The remote circuit breakers relay for 12v has been removed and I retained the 48 volt relay and rewired it to hook up to the SMA SI or the BMS to act as a load shed relay. The input to the remote circuit is AC1 and the output goes to one of the other 50amp breaker for the LOADS. And this obviously goes to the loads buss bar.
The pre-charger cicuit sits top left and I connected the contactor directly to the DC breakers (which now have a pin in them so they move together) ... The red L2 buss bars have been removed and a din rail was placed in there for the Batrium BMS and expansion board ... I put 3 extra din rail fuse holders for that circuit bottom left near the existing din relay.
The neutral bar is no longer grounded, and the negative bus bar has been replaced with a short one and rotated to make it fit in the space I had as I had to replace the existing buss bar which was incompatible with the batrium shunt sensor. The following image doesn't show current state as I have everything wired up less the external sources (SMA COMM / Relay / inputs / outputs, Battery inputs / balancer) ... but this image is clearer as I haven't cleaned up wires yet since I need two more cables before continuing.

Will update this as I make progress. I am waiting for a shield cat 8 22awg cable to come so I can chop it up and use it as my coms cable to the SI and for the batrium balancer to the core unit (since it is also shielded)
EDIT: the breakers on this unit say 50 amp but if you flip them over or look at the side (wherever the label is) it says they trip at 63amp ... was happy to see that)
Last edited: