Hello all,
First time poster! This has been a great forum and I've learned a ton.
I have two 48V LFP packs configured as 2PS16 using EVE LF280K cells, each configured with JK BMS (jk-bd6a20s10p). I had been running them as independent batteries tied together in parallel, but without any communication between them, connected to 2 x Sungoldpower SP6548 6.5kW inverters configured in parallel split-phase configuration (2P1/2).
I've been running this solar setup since 2019. It's worked fairly well, but since I've had no communication between the packs, and the inverters, I had to charge/discharge them using voltage, which is obviously not ideal with the flat-curve the LVP cells have. It's been tough to change the depth of discharge seasonally, hence why I finally was ready to start getting SOC average of both packs.
I recently upgraded my BMS on both of my packs to the JK-PB2A16S-20P. Before install, thanks to @Off-Grid-Garage 's absolutely awesome tutorials and settings, upgraded my BMS firmware to V15.41. I installed them over the weekend, but immediately noticed that the SOC calculation is way off. One of the packs was around 96% prior to replacement of the BMS, but after using the latest settings (under JK Inverter BMS JK-PBxx) on @Off-Grid-Garage https://off-grid-garage.com/my-settings/ page. After applying those settings, the first pack read 70%. Similarly after upgrading the second pack, got a similar reading. I had hoped that after a couple of days, it would charge fully, but they didn't.
So here's my issues:
1. SOC is reporting totally inaccurately
2. BMS communication between packs via RS485 shows "Bulk charging", but only 1 pack at address 0 is showup up in the JK Monitor software (v2.7).
3. My inverters, which uses RS485 for BMS communication, using the PYLON settings, times out after 3 minutes and gives a error code 61.
Let me detail my setup for clarity.

Using the included cables with the inverter (INV -> BAT) with the appropriate pins (3,5 -> 1,2) connected to the right set of ports, in port 1, or RS485-2 in the above diagram. I was able to do the firmware upgrade, so I know that I'm getting good communication with each BMS.
Both BMSs are configured as such: Master -> 0 (DIP 0000), Slave -> 1 (1000). The Inverter is plugged in with the above cable in RS485-1 with the cable mentioned above. The laptop to monitor things is connected to RS485-2, then the slave is connected from the master's RS4852 (right-port) to the slave's RS485-2 (left-port)
For inverter communication, the (INV -> BAT) is connected, as mentioned above, but only connected to the 2P1 inverter in the Battery RS485 port on the left. The black cable is connected to an OrangePI running Solar assistant.
The batteries negatives are connected from the negative to the BMS, BMS is connected to a bus connection, then to a Victron SmartShunt then to each inverter. The positives are connected from the positive to 200A breakers (one for each pack) then direct then a 1+2,1,2 DC switch, then split to each inverter.
Here's the master:

Slave:

PC connection:

Battery that was ~90% IIRC, but this was SOC after upgrade:

This is the error code and settings:


I tried today to validate that the communication between batteries were working, but the JK Monitor software is only able to see the first battery, no second.

As you can see in my software, only Device 0 shows.

I've attached PDFs for my inverter and EVE cells.
Any help or advice would be much appreciated! I can provide my old BMS configurations if needed. Thanks in advance!
First time poster! This has been a great forum and I've learned a ton.
I have two 48V LFP packs configured as 2PS16 using EVE LF280K cells, each configured with JK BMS (jk-bd6a20s10p). I had been running them as independent batteries tied together in parallel, but without any communication between them, connected to 2 x Sungoldpower SP6548 6.5kW inverters configured in parallel split-phase configuration (2P1/2).
I've been running this solar setup since 2019. It's worked fairly well, but since I've had no communication between the packs, and the inverters, I had to charge/discharge them using voltage, which is obviously not ideal with the flat-curve the LVP cells have. It's been tough to change the depth of discharge seasonally, hence why I finally was ready to start getting SOC average of both packs.
I recently upgraded my BMS on both of my packs to the JK-PB2A16S-20P. Before install, thanks to @Off-Grid-Garage 's absolutely awesome tutorials and settings, upgraded my BMS firmware to V15.41. I installed them over the weekend, but immediately noticed that the SOC calculation is way off. One of the packs was around 96% prior to replacement of the BMS, but after using the latest settings (under JK Inverter BMS JK-PBxx) on @Off-Grid-Garage https://off-grid-garage.com/my-settings/ page. After applying those settings, the first pack read 70%. Similarly after upgrading the second pack, got a similar reading. I had hoped that after a couple of days, it would charge fully, but they didn't.
So here's my issues:
1. SOC is reporting totally inaccurately
2. BMS communication between packs via RS485 shows "Bulk charging", but only 1 pack at address 0 is showup up in the JK Monitor software (v2.7).
3. My inverters, which uses RS485 for BMS communication, using the PYLON settings, times out after 3 minutes and gives a error code 61.
Let me detail my setup for clarity.

Using the included cables with the inverter (INV -> BAT) with the appropriate pins (3,5 -> 1,2) connected to the right set of ports, in port 1, or RS485-2 in the above diagram. I was able to do the firmware upgrade, so I know that I'm getting good communication with each BMS.
Both BMSs are configured as such: Master -> 0 (DIP 0000), Slave -> 1 (1000). The Inverter is plugged in with the above cable in RS485-1 with the cable mentioned above. The laptop to monitor things is connected to RS485-2, then the slave is connected from the master's RS4852 (right-port) to the slave's RS485-2 (left-port)
For inverter communication, the (INV -> BAT) is connected, as mentioned above, but only connected to the 2P1 inverter in the Battery RS485 port on the left. The black cable is connected to an OrangePI running Solar assistant.
The batteries negatives are connected from the negative to the BMS, BMS is connected to a bus connection, then to a Victron SmartShunt then to each inverter. The positives are connected from the positive to 200A breakers (one for each pack) then direct then a 1+2,1,2 DC switch, then split to each inverter.
Here's the master:

Slave:

PC connection:

Battery that was ~90% IIRC, but this was SOC after upgrade:

This is the error code and settings:


I tried today to validate that the communication between batteries were working, but the JK Monitor software is only able to see the first battery, no second.

As you can see in my software, only Device 0 shows.

I've attached PDFs for my inverter and EVE cells.
Any help or advice would be much appreciated! I can provide my old BMS configurations if needed. Thanks in advance!
Attachments
Last edited: