Integra Rack Ground Mount System, Fuses but no combining, 4 Pole DC disconnect

pgrovetom

New Member
Joined
Dec 20, 2019
Messages
42
I was looking at the Integra Rack IR30 or IR45 using the ballast method of holding it down. Has anyone used it with compacted road base below and using 3/4 drain rock for the ballast? How many inches of compacted road base did you require? Any opinions

I was looking at bringing 3 strings of 14 panels each ( maybe 15 will be ok) on 3 pairs of #8 Red/Black wire plus a green #10 ground. All the Integra Racks will be tied together along with the 3x14 panels using #6 bare copper wire and tied to the ground wire in the conduit. I'm looking to utilize a box similar to a combiner box at the racks to fuse the 3 strings and interconnect the solar string wires and ground to the underground conduit wiring but do not need combining. I want to bring all 3 strings back without any combining to a EG4 18 inverter's 3 MPPT inputs. Do they make combiner like boxes located at the array with fuses per string that allow the gauge wire and type transitions but do not combine any of the strings? They just pass through fused and transition to underground THWN-2 wire in the conduit. Could anyone suggest a good model capable of this? Or do they make combiner boxes where the combining can be disabled by removing a jumper or something like that?

I have determined that the 3 string wire sets arriving at the home do require a DC disconnect outside the home so a fire fighter could shut down the 500v + DC arriving from the panels. Most of the non inverter DC disconnects that meet outdoor requirements handle to poles or 2 strings. Does anyone know of a good outdoor high quality DC disconnect that can handle 13 AMPs per string pair for 3 pairs ( or 4 with one unused would be fine).

thanks for any ideas in advance,
 
In the US the home supply stores electrical section have carlton plastic boxes that have no cut-outs that you add cut-outs to as needed. They have various sizes. I have a 4x4 and added 5 grommet holes (for the 5 wires for 2 strings-2red/2black/1ground) and then a 1" spot to connect to the conduit to go back to the house.

https://images.thdstatic.com/catalog/pdfImages/9e/9e257276-621e-4429-b3df-cee19c2b366f.pdf (page 49 listed at the bottom).

If you only have one string per mppt input (and are not using pv#1/pv#2 combiner on mppt input #1) then you do not need fuses as the solar panels don't have any possible way to fault and go over 20A.

On my calculation with the lowest VOC panels I could find 14 panels was going to be right on the edge of too much voltage when the outside temp was my targeted min of -15F, if you do not have a risk of that low of temp 14 at VOC of around 37 should work.
 