I have a new Sol-Ark 15k, and it seemed to randomly go off grid for a few minutes. I finally figured out it was because of L1 and L2 voltage changes.

Normally, L1 and L2 track within 0.5v of each other, varying between 120.0-121.0v on average. When the inverter detaches from the grid, the spread between L1 and L2 abruptly widens out to 3v, but the total still seems to be around 240v (L1 could be 119.0 and L2 would be 122.5v).

Do other people see similar situations? I'm tinking it is ok to stay off grid becuase the grid may be having issues when the divergence happens. There may also be something funky about the power that it sees that is not evident in the voltage log. Note: Frequency stays rock solid.
 
You may have a poor connection in neutral.
I wouldn't expect that slight voltage variation itself to be a problem or cause disconnect. It may instantaneously jump much farther.

If you were to apply a large 120V load (e.g. a few space heaters), then you could probe with DMM, look for voltage drop across contacts. After a long time, it could also show up as heat.
 
You may have a poor connection in neutral.
I wouldn't expect that slight voltage variation itself to be a problem or cause disconnect. It may instantaneously jump much farther.

If you were to apply a large 120V load (e.g. a few space heaters), then you could probe with DMM, look for voltage drop across contacts. After a long time, it could also show up as heat.
Where do I look. The grid side L1-L2 differential continues even after Sol-Ark disconnects from the Grid. Whatever is happening is either:
1) Grid side; or
2) Inside the Sol-Ark where is measures Grid Voltage.

I could expose the Grid Lines and take a reading the next time it happens. See if it is real, or Sol-Ark problem.
 
Do you have loads which don't pass through SolArk? If so, you could try loading heavily, see if it changes a lot, try to track down where.

The problem could come from grid if neutral has a problem there. Ideally have continuous monitoring which logs highest/lowest voltages seen.

Does SolArk log/report what it saw which was out of spec?
 
Sol-Ark was reporting Grid Voltages of 120 and 124 for L1 and L2 (on its screen). I measured grid voltages on the Sol-Ark Grid Terminals and saw 122 and 122. So there was a problem with the Sol-Ark's Grid Circuits.

I called my installer, and he was stumped (he was able to pull the inverter logs and status). He said to call Sol-Ark. It was after hours on Friday, so I couldn't talk to anyone from support. Since it was needlessly draining the batteries, tried to turn off the sol-ark, but it would just turn off, and stayed disconnected from the grid. I powered back up, and during a short period where it reconnected to the Grid, I flipped the sol-ark battery breakers to turn off the battery. At that point, it stayed connected to the Grid and objected (had no where else to get power from). A few hours later, the problem resolved itself, warning message went away, and I reconnected the batteries to charge them back up.

I talked to Sol-Ark Monday morning. They said I had one of the early 15k's with the original firmware. He said there was a known grid problem in the software, and said an update would take care of it. I asked for the details (what conditions caused the software glitch), but he didn't know. We shall see.
 
Old thread, but has this problem come back for you? I've got a year old Sol-Ark 15k with fully up-to-date firmware with the same issue. There doesn't seem to be any rhyme or reason for it (no big loads). Periodically, the inverter will see the voltage difference between L1 and L2 at the grid go from something like 0.5v to 3v and disconnect from the grid for a minute or so. Kind of hard to troubleshoot with no error messages or way to reproduce the issue.
 
I have not yet setup logging, so I can't say if the problem has persisted. It does randomly go off grid for a few minutes. But most of the time it is during a weather event, so it might be working as expected. I haven't had the prolonged problem (off grid for more than a few minutes when the grid was up), so that problem has gone away.
 
Today, Sol-Ark emailed me and told me they had changed my Grid parameters to, hopefully, fix this issue. The problem is that I'm selling energy back to my utility and I was under the impression that I HAD to be using UL1741SB as my Grid Mode to do that AND changing parameters only works under General mode. To accommodate that, he changed me to Grid mode.

Am I allowed to sell back under General mode instead of UL1741SB? If so, what are the repercussions of doing that? I've written them back to ask, but it might be a while before they get back to me.

EDIT: It's full of stuff I don't understand, but this web page:


says the differences between (what I believe is) "General" mode and later modes (SA and SB) are:

"UL 1741-SA was published in conjunction with California Rule 21 Phase 1 requirements. These safety tests certify the “smart inverter” grid support functionality needed to modernize the grid through widespread DER integration. The testing requirements for UL 1741-SA are as follows:
  • Anti-islanding
  • Low/high-voltage ride-through (L/HVRT)
  • Low/high-frequency ride-through (L/HFRT)
  • Specified power factor (SPF)
  • Volt/VAR mode
  • Volt/Watt mode
  • Frequency/Watt mode
  • Ramp rate
UL 1741-SB introduced an interoperability conformance test in accordance with IEEE 1547.1-2020. Conformance can be achieved through either DNP3, IEEE 2030.5, or SunSpec Modbus communications protocols, which are used to store or send information and to control adjustable inverter functions. The testing requirements for UL 1741-SB are more stringent and include the following in addition to the requirements defined above for UL 1741-SA certification:
  • Watt/VAR mode
  • Voltage magnitude and time trip
  • Frequency magnitude and time trip
  • EMI
  • Surge
  • Rate of change of frequency (ROCOF)
  • Dynamic voltage support
  • Enter service
  • Synchronization
  • Open phase
  • Harmonics
  • DC injection
  • Ground fault overvoltage (GFOV)
  • Load rejection overvoltage (LROV)
  • Prioritization of DER responses
  • Fault current
  • Persistence of DER parameter setting"
But, I don't know what that means in Joe Bag o'Donuts English.
 
Last edited:
I'll try to fit Sol-ark's changes to my Grid Settings in the following posts (once again, I don't know what they mean, if they're correct or if they'll solve the 1 minute disconnect issue). I had to break this up to fit into what's allowed here.

Besides the Grid Mode, there's no change on the Grid Selection tab.

SettingUL1741SBGeneral
Grid Selection tab
Grid ModeUL1741SBGeneral Standard
Grid Frequency60Hz60Hz
Single Phase Check BoxUncheckedUnchecked
120/240V Split Phase Check BoxCheckedChecked
120/208V 3 Phase Check BoxUncheckedUnchecked
Grid Reconnect Time60s60s
Power Factor11
Fixed Q0.00%0.00%
Q_Response10s10s
Output V120/240V120/240V
Output V++0V+0V
 
Last edited:
Here's the Connect tab. To me, it looks like they've narrowed the normal connection voltage range and increased the reconnection range. The frequency ranges are both increased:

SettingUL1741SBGeneral
Connect tab
Reconnect Grid Vol High263.8V288.0V
Reconnect Grid Vol Low211.4V120.0V
Reconnect Grid Hz High61.5Hz65.0Hz
Reconnect Grid Hz Low58.5Hz55.0Hz
Reconnect Ramp Rate60s60s
Normal Connect Grid Vol High288.0V265.0V
Normal Connect Grid Vol Low120.0V185.0V
Normal Connect Grid Hz High62.0Hz65.0Hz
Normal Connect Grid Hz Low57.0Hz55.0Hz
Normal Ramp Rate60s60s
 
Last edited:
Here's the IP tab. This one looks weird. Lowered the Over Voltage amount, mostly lowered the HV (high voltage?) numbers, mostly increased the LV (low voltage?) numbers, and increased the acceptable frequency ranges. But, the really odd thing is the change to the number of seconds in those numbers. My old UL1741SB settings show 5 of those times in many multiple seconds. The new General ones are all sub-seconds. HF1 and LF2, for example, went from 299 seconds (basically, 5 minutes) to 0.29s (1000 times less):

SettingUL1741SBGeneral
IP tab
Over Voltage U>(10 min. running mean)276.0V260.0V
HV3288.0V265.0V
HV2288.0V – 0.16s265.0V – 0.10s
HV1264.0V – 13.00s265.0V – 0.13s
LV1211.2V – 21.00s185.0V – 0.21s
LV2168.0V – 2.00s185.0V – 0.20s
LV3120V185.0V
HF362.00Hz65.00Hz
HF262.00Hz – 0.16s62.00Hz – 0.10s
HF161.50Hz – 299.00s62.00Hz – 0.29s
LF158.50Hz – 299.00s57.00Hz – 0.29s
LF257.00Hz – 0.16s57.00Hz – 0.10s
LF357.00Hz55.00Hz
 
Last edited:
Here's the F(W) tab. First, the F(W) Check Box is now UNchecked instead of checked. Does that mean these settings aren't being used? But, the numbers show an increase in the allowed frequency ranges:

SettingUL1741SBGeneral
F(W) tab
F(W) Check BoxCheckedUnchecked
Over Frequency Droop F>40% PE/Hz40% PE/Hz
Over Frequency Start Freq F60.50Hz65.0Hz
Over Frequency Start Delay0.00s0.00s
Over Frequency Stop Freq F60.50Hz65.0Hz
Over Frequency Stop Delay0.00s0.00s
Under Frequency Droop F>40% PE/Hz40% PE/Hz
Under Frequency Start Freq F>59.50Hz55.00Hz
Under Frequency Start Delay F>0.00s0.00s
Under Frequency Stop Freq F>59.50Hz55.0Hz
Under Frequency Stop Delay F>0.00s0.00s
 
Last edited:
Here's the V(W) / V(Q) tab. In both cases, the V(W) and V(Q) Check Boxes are UNchecked. Again, does this mean the settings don't apply? Unfortuantely, I don't understand what these numbers are saying at all:

SettingUL1741SBGeneral
V(W) / V(Q) tab
V(W) Check BoxUncheckedUnchecked
Response_T5s10s
V1 / P1110.0% / 100%109.0% / 100%
V2 / P2111.0% / 50%110.0% / 20%
V3 / P3112.0% / 0%111.0% / 20%
V4 / P4112.0% / 0%111.0% / 20%
V(Q) Check BoxUncheckedUnchecked
L.In / L.Out20.0% / 5.0%20.0% / 5.0%
V1 / Q190.0% / 43%90.0% / 44%
V2 / Q294.0% / 0%95.7% / 0%
V3 / Q3106.0% / 0%104.3% / 0%
V4 / Q4110.0% / -43%112.2% / -60%
 
Last edited:
And, here's the P(Q) / P(F) tab. No change. But, the P(Q) and P(F) Check Boxes are all UNchecked. Not applied?:

SettingUL1741SBGeneral
P(Q) / P(F) tab
P(Q) Check BoxUncheckedUnchecked
P1 / Q120% / 20%20% / 20%
P2 / Q2100% / 20%100% / 20%
P3 / Q3100% / 20%100% / 20%
P4 / Q4100% / 20%100% / 20%
P(F) Check BoxUncheckedUnchecked
L.In / L.Out50.0% / 100.0%50.0% / 100.0%
P1 / F150% / 1.00050% / 1.000
P2 / F2100% / 0.800100% / 0.800
P3 / F3100% / 0.800100% / 0.800
P4 / F4100% / 0.800100% / 0.800
 
Last edited:
Today, Sol-Ark emailed me and told me they had changed my Grid parameters to, hopefully, fix this issue. The problem is that I'm selling energy back to my utility and I was under the impression that I HAD to be using UL1741SB as my Grid Mode to do that AND changing parameters only works under General mode. To accommodate that, he changed me to Grid mode.

Am I allowed to sell back under General mode instead of UL1741SB? If so, what are the repercussions of doing that? I've written them back to ask, but it might be a while before they get back to me.
I would phrase it a little differently. If you sell back, then they can make you comply with UL1741SB. More a quid-pro-quo than selling under UL1741SB. What UL1741SB does is requires your inverter to stay connected to the grid during fairly wide grid problems. That is to avoid destabilizing the grid when the Power Companies are trying to balance generation and consumption. For example, if you are exporting to the grid, and the grid voltage drops to 185v, you have to stay connected for whatever time frame is required. They don't want your generation to go offline when Power Generators can produce (or can't wheel) enough power. Similarly, if the grid is over voltage, you have to stay connected to soak up the excess production.

I haven't read UL1741SB, but it seems odd that whether you have to stay connected is not tied to whether you are net consuming or net producing ok to disconnect when undervoltage if you are net consuming, or ok to disconnect when over voltage and you are net producing.
 
I guess it's become a moot point. At 10:30 am, I had the same 1 minute disconnect that I had with my UL1741SB settings. So, it doesn't look like these changes have helped.

In their email to me, Sol-ark said it might take 24 hours for the changes to take effect (it's been 16 hours). But, I can't see why that would be. Unfortunately, that mini-outage didn't get captured by the inverter's periodic data update. So, I can't send it to Sol-ark. But, I'm pretty sure I'm just going to flip the Grid Mode back from General to UL1741SB. I assume any parameter changes will revert since they can only be changed under General mode.

EDIT: Yep. When I switched back from General to UL1741SB, it reset all the Grid parameters back to default. So, I'm good. I guess I'll just live with the periodic flicker of lights and computer UPS ramping up when these 1 minute disconnects happen. Of course, if we didn't have batteries connected to the solar system, that would be a different matter.
 
Last edited:
It's odd that I always get these disconnects when the inverter shows a 3v difference between the grid legs. I'm wondering if the inverter is seeing a much bigger difference (enough to actually exceed the grid settings), disconnecting because of that, but not showing that actual difference on the LCD or on MySolark. But, then, it also never shows an alert that something out of spec happened and it recovered.
 
Have you looked at the grid frequency? I have seen similar things in these boxes when the grid freq will suddenly show a drop to zero for just a split second. You have to catch it in the logs.

I have also seen what you are explaining when there is a UPS in use in the house. Sol-Ark has also mentioned these can cause some kind of feedback as they put it that can cause a voltage spike like you describe.

The adjustments that Sol-Ark (tried) was to simply broaden the allowable low and high grid frequency before a disconnect. I personally feel this is something they know they have a problem with but have yet to find a real solution since they are so quick to make this change anytime someone calls in.
 
I guess it's become a moot point. At 10:30 am, I had the same 1 minute disconnect that I had with my UL1741SB settings. So, it doesn't look like these changes have helped.

In their email to me, Sol-ark said it might take 24 hours for the changes to take effect (it's been 16 hours). But, I can't see why that would be. Unfortunately, that mini-outage didn't get captured by the inverter's periodic data update. So, I can't send it to Sol-ark. But, I'm pretty sure I'm just going to flip the Grid Mode back from General to UL1741SB. I assume any parameter changes will revert since they can only be changed under General mode.

EDIT: Yep. When I switched back from General to UL1741SB, it reset all the Grid parameters back to default. So, I'm good. I guess I'll just live with the periodic flicker of lights and computer UPS ramping up when these 1 minute disconnects happen. Of course, if we didn't have batteries connected to the solar system, that would be a different matter.
My default grid mode is SRD-UL1741 and I'm able to make changes to grid parameters.
 
Usually, the grid frequency remains at its normal, solid 60hz. Occasionally, I do see rare instances where the frequency drops to 0. In those cases, I assume the grid actually has hiccupped and gone down momentarily. Of course, part of the problem in figuring out what's going on is that the outages are only 1 minute long. So, they tend not to get captured in the logs where data capture happens only every 5 or 10 minutes. Besides those rare frequency drops to 0, I've never seen any swings in the other electrical characteristics wide enough to cause a disconnect. I sure wish the inverter would record an alert when these happen.

About feedback from the computer's UPSes, I'd actually considered that. But, I just couldn't see a way anything those tiny UPSes would do could be fed back into the house circuits at a level high enough to mess with the inverter's perception of the grid's voltage. It should be monitoring the incoming house circuit levels. But, there shouldn't be anything going back out to it.

@Oldphile I think that's why Sol-ark changed my grid settings from UL1741SB to General mode.
 