WorldwideDave
Solar Addict
12V system. 200Ah custom battery. In plastic box with 5 sides (top open), and on a wood shelf with 4 sides open (one side is open for fresh air, and the top is open for about 8" above the battery cells and BMS).
My system has 2 battery sensors. One connected to Victron GX, and the other a Ruuvi temp sensor, just to compare.
I turn off all MPPTs.
Using AC/DC charger, I ensure both Victron Shunt reads 100% SOC, and the internal battery BMS (JBD) reads 100% SOC. The charger reads float, all is good.
At the beginning of the day, the ambient temperature is 11.5 degrees C.
Both temp sensors report around this temperature (12-13 degrees C) before any loads run.
I then turn on my non-victron inverter, and run a load at 160 Amps discharge. The pool pump runs for an hour at 3450 RPM, no problem. Around the 90 minute mark, Cerbo GX reports a low state of charge, followed by low voltage, and the BMS reports 0% SOC as well, and the voltage I think hits 11 volts and inverter beeps, so I shut off the load, and wait for inverter to cool, then shut off the inverter, and done with discharge test.
During test the temps go up to 38 degrees C max, or about 100 degrees F. No big deal.
I then wait another 90 minutes, but temp has barely gone down. It is still around 21C outside, but the temp sensors are still up at 30C. That is 9C or 48.2F difference from outside temp.
No the inverter isn't in the same space.
It seems to me it should be cooling faster than it is.
So after this discharge test is done, I leave the inverter off, I turn on AC/DC charger (25A victron), and turn on 3 MPPTs (2 victron, 1 non-victron) and pump as many amps as possible into the BMS to see what happens. First time ever charging at over 70 A - was exciting.
Peak amperage to the battery was 116 A which may not be super exciting to most of you, but my system used to overheat with anything over 45 A charging. Swapped BMS, FYI.
Anyway, as you can see below, the temps did rise, but only up to 36 degrees C. The sun was setting so that ended this test. The higher the amps charging (or discharging) the higher the temps would get at the battery.
This shows me that temps rise whether charge or discharge. Assumed that, but wanted to prove it.
However, even after turning the PV and charger back off, it has been 2 hours, and it still hasn't gone down below 32 degrees C.
Is this normal? Is this unexpected?
It is currently 14 degrees C outside right now. Temp sensors are twice that.
Just seeing if this is what I should expect - they don't cool down to ambient super fast.
I of course could add a D/C fan to blow air through the battery compartment/box, but if I don't need to worry about it - because my temp sensor is not reporting over 50 C - then I guess I will just let it go.
My plan is to discharge now to dead, then at peak sun tomorrow, charge again from cold and report back.

My system has 2 battery sensors. One connected to Victron GX, and the other a Ruuvi temp sensor, just to compare.
I turn off all MPPTs.
Using AC/DC charger, I ensure both Victron Shunt reads 100% SOC, and the internal battery BMS (JBD) reads 100% SOC. The charger reads float, all is good.
At the beginning of the day, the ambient temperature is 11.5 degrees C.
Both temp sensors report around this temperature (12-13 degrees C) before any loads run.
I then turn on my non-victron inverter, and run a load at 160 Amps discharge. The pool pump runs for an hour at 3450 RPM, no problem. Around the 90 minute mark, Cerbo GX reports a low state of charge, followed by low voltage, and the BMS reports 0% SOC as well, and the voltage I think hits 11 volts and inverter beeps, so I shut off the load, and wait for inverter to cool, then shut off the inverter, and done with discharge test.
During test the temps go up to 38 degrees C max, or about 100 degrees F. No big deal.
I then wait another 90 minutes, but temp has barely gone down. It is still around 21C outside, but the temp sensors are still up at 30C. That is 9C or 48.2F difference from outside temp.
No the inverter isn't in the same space.
It seems to me it should be cooling faster than it is.
So after this discharge test is done, I leave the inverter off, I turn on AC/DC charger (25A victron), and turn on 3 MPPTs (2 victron, 1 non-victron) and pump as many amps as possible into the BMS to see what happens. First time ever charging at over 70 A - was exciting.
Peak amperage to the battery was 116 A which may not be super exciting to most of you, but my system used to overheat with anything over 45 A charging. Swapped BMS, FYI.
Anyway, as you can see below, the temps did rise, but only up to 36 degrees C. The sun was setting so that ended this test. The higher the amps charging (or discharging) the higher the temps would get at the battery.
This shows me that temps rise whether charge or discharge. Assumed that, but wanted to prove it.
However, even after turning the PV and charger back off, it has been 2 hours, and it still hasn't gone down below 32 degrees C.
Is this normal? Is this unexpected?
It is currently 14 degrees C outside right now. Temp sensors are twice that.
Just seeing if this is what I should expect - they don't cool down to ambient super fast.
I of course could add a D/C fan to blow air through the battery compartment/box, but if I don't need to worry about it - because my temp sensor is not reporting over 50 C - then I guess I will just let it go.
My plan is to discharge now to dead, then at peak sun tomorrow, charge again from cold and report back.