Hey everyone,
I need some advice on properly configuring my solar setup. I’m using an MPPSolar Inverter PIP3024GK and a Victron SmartSolar 100/50 MPPT, both connected to a 24V 300Ah LiFePO4 battery bank consisting of three Power Queen 25.6V 100Ah batteries (I've used 4x Ultimatron 100Ah 12V Gel batteries in the past).
I've set both MPPSolar and Victron MPPT to the same charging parameters to avoid conflicts:
One battery seems to handle this fine, but two of them have a new issue:
I need some advice on properly configuring my solar setup. I’m using an MPPSolar Inverter PIP3024GK and a Victron SmartSolar 100/50 MPPT, both connected to a 24V 300Ah LiFePO4 battery bank consisting of three Power Queen 25.6V 100Ah batteries (I've used 4x Ultimatron 100Ah 12V Gel batteries in the past).
Initial Battery State & Charging Setup:
Before connecting everything, I checked the battery voltage—all three were at 26.1-26.2V (35-40% SoC, according to the battery manual). I decided to charge them individually first before wiring them together to ensure a well balance.I've set both MPPSolar and Victron MPPT to the same charging parameters to avoid conflicts:
- Bulk (Absorption): 28.4V
- Float: 27.6V
- MPPSolar: 10-20A (handles a free-standing 3kW solar array)
- Victron: 15A (handles a 460W solar tracker, planning to upgrade to 1100W soon, meaning higher charge current)
Both are connected to the battery bank through a Victron Power In.
The Issue:
Once the battery voltage exceeds float, the MPPSolar stops charging in Bulk, leaving only the Victron SmartSolar to handle Bulk and Absorption.One battery seems to handle this fine, but two of them have a new issue:
- When Victron enters Absorption Mode, the voltage spikes to 30V, triggering the BMS shutdown.
- I’m unsure if this is due to high charging current or if my Absorption Voltage was set too high from the start.
Battery Manufacturer’s Specs:
- Recommended Absorption Voltage: 28.8V (± 0.4V) - 29.2V
- Recommended Charging Current (per battery): 20A
- Maximum Recommended Charging Current: 50A (up to ~96% SoC)
My Questions:
- What are the best Absorption, Float, and Charge Current settings for a LiFePO4 bank (24V 300Ah) when using two charge controllers?
- Does the voltage spiking to 30V, then dropping to Float, then back to Bulk (and repeating) indicate a fully charged battery, or is it a sign of incorrect settings? Could this be due to the Re-bulk setting being at the default 0.1V?
- Is it normal for Absorption time to be extremely short for one battery? Absortion Time is set to 1 hour with Tail Current on 1A. Charging current drops from 15A to 1A in just 10-15 minutes.