Hello,
A while ago I watched Will's youtube video on JBD Smart BMS and it looked nice so I purchase 2 of them (12v 4s 120A) from aliexpress
https://www.aliexpress.com/item/4000425316662.html?spm=a2g0s.9042311.0.0.27424c4dTRne5e
for 2 LiFePo4 banks.
After the prep work (crimping, top balancing, etc), One BMS works well but I found the other one shows wrong voltage for cell 3 and 4, as shown in the screenshot. I also observed that the shown voltages for cell 3 and 4 fluctuates very quickly(~ +-0.01v) compared to the other battery bank, which fluctuates way slower. I have done the following for diagnose -
- Checked all connectors made sure they are properly tightened.
- Use multimeter and measured voltage, readings are correct, which is different from BMS reading (delta are ~ 0.002 between cells), note I took readings from battery's metal connector directly, the top of the screws and balance wire ring connectors just to make sure I don't have connector issues.
- I swapped cell 3 and 4, same result - any cell in position 3 are showing higher voltage than the cell in position 4.
- I swapped balance cable from the other BMS that worked properly. same wrong result.
At this point I think the BMS is faulty. I suspect the balance circuit might have contact issues.
Wondering if there is anything else I can do to diagnose this. I have contacted the seller but they are not being very helpful yet
A while ago I watched Will's youtube video on JBD Smart BMS and it looked nice so I purchase 2 of them (12v 4s 120A) from aliexpress
https://www.aliexpress.com/item/4000425316662.html?spm=a2g0s.9042311.0.0.27424c4dTRne5e
for 2 LiFePo4 banks.
After the prep work (crimping, top balancing, etc), One BMS works well but I found the other one shows wrong voltage for cell 3 and 4, as shown in the screenshot. I also observed that the shown voltages for cell 3 and 4 fluctuates very quickly(~ +-0.01v) compared to the other battery bank, which fluctuates way slower. I have done the following for diagnose -
- Checked all connectors made sure they are properly tightened.
- Use multimeter and measured voltage, readings are correct, which is different from BMS reading (delta are ~ 0.002 between cells), note I took readings from battery's metal connector directly, the top of the screws and balance wire ring connectors just to make sure I don't have connector issues.
- I swapped cell 3 and 4, same result - any cell in position 3 are showing higher voltage than the cell in position 4.
- I swapped balance cable from the other BMS that worked properly. same wrong result.
At this point I think the BMS is faulty. I suspect the balance circuit might have contact issues.
Wondering if there is anything else I can do to diagnose this. I have contacted the seller but they are not being very helpful yet