Hello
I have just build my last battery (for now). In total i have 4, in Yixiang V.2 enclosures, with JK inverter BMS V.19. I have updated to firmware 19.10, The first tree went fine, and communication was working from start. Today i had so many problems with the fourth pack. First it interrupted all the communication on the RS485-2 ports. After fidelling a lot with it changed cables and so on, I saw that UART 2 ( The one that is chosen by the bms it self) was set to 1 JK BMS 485 on the 2 slaves that worked but on battery 4 (adress 3) it was set to the 4g protocol. Then I set UART 1 to protocol 1 JK BMS 485 and connected Battery 4 (adress 3) RS485 -1 to Battery 3 (adress 2) RS485-2. The made the pack work! Not the intended connection, but it confirmed my theory about UART 2 protocol being wrong)
Any ideas?
Regards Tommy
I have just build my last battery (for now). In total i have 4, in Yixiang V.2 enclosures, with JK inverter BMS V.19. I have updated to firmware 19.10, The first tree went fine, and communication was working from start. Today i had so many problems with the fourth pack. First it interrupted all the communication on the RS485-2 ports. After fidelling a lot with it changed cables and so on, I saw that UART 2 ( The one that is chosen by the bms it self) was set to 1 JK BMS 485 on the 2 slaves that worked but on battery 4 (adress 3) it was set to the 4g protocol. Then I set UART 1 to protocol 1 JK BMS 485 and connected Battery 4 (adress 3) RS485 -1 to Battery 3 (adress 2) RS485-2. The made the pack work! Not the intended connection, but it confirmed my theory about UART 2 protocol being wrong)