It all depends on the cells you have. If the cells are over 200AH then use a 200A BMS and Keep It Sweet & Simple !(BMS is not enclose)
So you’d recommend 100A instead of the 200A version?
I want to be able to charge it with two or three 60A SCCs so I figured I should go with the 200A version.
I only have 16cells
Remember that Standard LFP can discharge happily at 1C and take 0.5C Charge. The 200A BMS will let you draw up to a max of 200A and charge at 100A ). Just because the BMS & Battery Pack "can" deliver 200A it does not mean it has to. For example with my 7 Packs with 200A BMS', none of them ever see heavy loading as such but each pack can carry the load on it's own if necessary. The heaviest household load my system "may see rarely" is between 150-175 Draw and for only a short period of time.
Also a note, that a 4S, 8S or 16S can deliver 200A but the length of time of course is affected by the pack Size & Voltage