"MF" or maintenance free is simply a FLOODED lead-acid "sloshy", that knowing that the typical consumer won't check or add water as needed, is filled with more electrolyte than normal at the factory, and sealed up. The hope is that this will take the battery to the typical 4-year automotive life without the consumer having to check.Actually, the world of lead acid batteries is a bit more complicated than that. SLA also includes "Maintenance Free" or "Valve Regulated" batteries, that are actually just flooded lead acid batteries (yes, they slosh) that don't have caps for you to open and add water. I believe that most places I've seen refer to SLA as only the sealed version of the flooded, and AGM and GEL are separate.
I'm not sure this test really tells you much. You had a 55Ah AGM, and after you added 100Ah of LFP the amount of harvested energy and the morning resting voltage were higher. Well, yeah. If you would have added 100Ah of AGM, they would have been higher too.Here are the results of my first day of LFP+AGM.
For over a month, I have been charging the chassis 55Ah Optima AGM battery in the van from a 140W panel and through an MPPT SCC . I log stats at 5 min intervals. There was a pattern of morning Volts being around 12.6V just before sun-up. Also there was a pattern of about 0.4A charge current with total daily of around 5Ahs. The AGM runs a dashcam 24/7.
On Oct 11:
Just prior to sun-up, the SCC read the AGM at 12.57V, a perfectly consistent value.
I then attached a 100Ah LFP at around 9:20AM. The LFP Volts had been measured by a clamp-on as 13.18V prior to attachment. Just prior to this attachment, the AGM had reached 13.9V and the SCC was in Float. The now new bank Volts dropped to a low of 13.28V for about 10 min. Then the SCC reverted into CC mode(Bulk) because it could not maintain the bank at the 13.5V float setting. Charging continued, and the SCC remained in bulk/CC until sundown.
The following morning, Oct 12, the SCC detected 13.21V just before sun-up. That is a gain of 0.64V. Also, Instead of the usual 5Ahs charge per day, the first day charging was 35Ahs.
I will be moving the LFP into the trailer later to mate with a 100AH AGM.
That I can get the AGM floated overnight for free?...
Unless I'm missing the point. What do you think this test told you?
I think what would make your test much more interesting is to measure the current going in, out, and between the two during charging and discharging.
I guess there are different goals for different people in looking at this shotgun marriage of AGM with LFP. I think that some people see the toughness of the AGM as protecting the LFP: The LFP can be cut off by its BMS, but it won't cause a problem for the alternator because the AGM will step up and take it. I can't tell, but I think that some people are more familiar with AGM, and think they can dip their toe in the water by just slapping on some LFP.That I can get the AGM floated overnight for free?
I did measure the charge current once about 2 hours after they were joined. Each battery has a separate post on the bus bars. I did not parallel at the battery. My clamp on read 0.66A to the AGM and 4.10A to the LFP. That agreed with the total out from the SCC into the bus bars. I was pleased to see this imbalance because I want the LFP to get the majority of the charge. LFP has better charge efficiency and that avoids wasting daylight waiting for AGM to absorb. The LFP can take all night to float the AGM.
By keeping the AGM floated overnight, there is less need for absorption during solar hours. Hand-in-glove!
I would love to have automatic data logging of all of the current flows. I will have to settle for ad-hoc manual measurements.
I do suspect that one time only, right after connection, that the AGM transferred current to the LFP.
This LFP was acquired to be installed in the Travel Trailer. I am waiting on parts.
My 48V bank bulk charges at 56.4V and floats at 54.0V. That's right on spec for my bank.LFP doesn't like any of that. LFP is OK with being charged to full, but prefers to stay "between the knees" of 95% SoC and 10% SoC (or so). The preferred AGM bulk / absorption voltage for most brands is too high for an LFP bank.
Ding Ding Ding we have a winner!That I can get the AGM floated overnight for free?
I did measure the charge current once about 2 hours after they were joined. Each battery has a separate post on the bus bars. I did not parallel at the battery. My clamp on read 0.66A to the AGM and 4.10A to the LFP. That agreed with the total out from the SCC into the bus bars. I was pleased to see this imbalance because I want the LFP to get the majority of the charge. LFP has better charge efficiency and that avoids wasting daylight waiting for AGM to absorb. The LFP can take all night to float the AGM.
By keeping the AGM floated overnight, there is less need for absorption during solar hours. Hand-in-glove!
I would love to have automatic data logging of all of the current flows. I will have to settle for ad-hoc manual measurements.
I do suspect that one time only, right after connection, that the AGM transferred current to the LFP.
This LFP was acquired to be installed in the Travel Trailer. I am waiting on parts.
Yeah, I think we've been here before (like on the previous page of this thread). I am mostly unaware of any AGMs other than yours that this works for. I've never heard of or seen anything about your AGMs, other than the company's main business seems to be backup power for telecoms and such (with the exception of their acquisition of Outback). So I give you that your AGMs seem to fit better with LFP, but the discharge curve is still a slope vis the flat discharge curve of the LFP. So like I said - most of the energy will be between the AGMs and the LFPs, rather than to your loads and from your charging sources. I'm not certain of this, and would love to see some real world evidence to the contrary.My 48V bank bulk charges at 56.4V and floats at 54.0V. That's right on spec for my bank.
For a 16s LFP bank that would mean bulk charging at 3.525V/cell and floating at 3.375V/cell. That just seems a nice match.
I did check again at 6:00AM. I read -1.2A at the LFP neg cable. Given the 10 hours since the reading last night results in a total of -12Ahs.Well, not so fast. Sounds like @gelmjw will report back with more data on the current transients.
Besides, spending the money on an LFP battery just so it can get your AGM to float doesn't seem like "free".
That's very useful. Would love to see the charging side as well.This is an interesting graph of how the 2 chemistries behave during discharge. LFP at the bottom. Does not seem to be a lot of contribution from lead until the LFP is depleted.
Can you clarify please as I may not be interpreting "in reverse" in the way you intend.It's the same, but in reverse.