With high frequency inverters pushing more power and low frequency dropping in price, which would be better for an all electric house? Reminded that surge loads are high in a all electric house.
 
With high frequency inverters pushing more power and low frequency dropping in price, which would be better for an all electric house? Reminded that surge loads are high in a all electric house.
Either are fine. The surges come from inductive loads (motors). It doesn't matter if your heat source is electricity or gas, the motors are the same.
 
Either are fine. The surges come from inductive loads (motors). It doesn't matter if your heat source is electricity or gas, the motors are the same.
Does one outlast the other since the transformer can take the hit from a surge better than a Moffett? As for cost, the difference isn't much until you start calculations for surges. Can the grid boss be used with low frequency inverter to eliminate additional equipment?
 
Last edited:
In real world utility there is a term called system 'inertia'. This is the angular momentum of alternator rotors that can source or sink AC power with angular momentum. This helps the grid absorb positive or negative surge power. This includes what comes with poor power factor loads. It helps keep the utility grid stable.

HF inverters have little to no 'inertia'. What little inertia they provide comes from their HV DC filter capacitors. AC motor startup surge current is not the only consideration. Poor power factor inductive loads have a negative power flow for a portion of the AC cycle.

With poorer ability of HF inverters to absorb the momentary power back push, the result is spiking of the HV DC voltage or high ripple voltage on the HV DC bus. This is hard on the HV DC bus filter capacitors which have electrolytic type capacitors with ESR (effective series resistance) that heats the HV DC capacitors when there is a lot of AC ripple current. It can also result in battery to HV DC converter load instability.

HF inverters like Sol-Ark, Deye, and EG4 have a large bank of HV DC capacitors to improve the HF inverter's inertia.

Deye HV DC filter.jpg

LF inverters inherently have instantaneous bi-directional power flow capability, with back push power surges being pushed directly to batteries. This makes them have the appearance of strong 'inertia', assuming the battery is not at full state of charge where any back push can cause inverter DC input voltage to rise beyond maximum limit, causing inverter to shut down.

A lot of what the new regulations like Cal Rule 21 have to do with renewable energy systems feeding the grid providing a synthetic 'inertia' to the utility grid system.
 
HF here.
No issues running an entire house.
(10KW AIOs in parallel).
 

Attachments

  • Screenshot_2025-02-14-13-00-25-36_cbf47468f7ecfbd8ebcc46bf9cc626da.jpg
    Screenshot_2025-02-14-13-00-25-36_cbf47468f7ecfbd8ebcc46bf9cc626da.jpg
    52.7 KB · Views: 13
In real world utility there is a term called system 'inertia'. This is the angular momentum of alternator rotors that can source or sink AC power with angular momentum. This helps the grid absorb positive or negative surge power. This includes what comes with poor power factor loads. It helps keep the utility grid stable.

HF inverters have little to no 'inertia'. What little inertia they provide comes from their HV DC filter capacitors. AC motor startup surge current is not the only consideration. Poor power factor inductive loads have a negative power flow for a portion of the AC cycle.

With poorer ability of HF inverters to absorb the momentary power back push, the result is spiking of the HV DC voltage or high ripple voltage on the HV DC bus. This is hard on the HV DC bus filter capacitors which have electrolytic type capacitors with ESR (effective series resistance) that heats the HV DC capacitors when there is a lot of AC ripple current. It can also result in battery to HV DC converter load instability.

HF inverters like Sol-Ark, Deye, and EG4 have a large bank of HV DC capacitors to improve the HF inverter's inertia.

View attachment 278636

LF inverters inherently have instantaneous bi-directional power flow capability, with back push power surges being pushed directly to batteries. This makes them have the appearance of strong 'inertia', assuming the battery is not at full state of charge where any back push can cause inverter DC input voltage to rise beyond maximum limit, causing inverter to shut down.

A lot of what the new regulations like Cal Rule 21 have to do with renewable energy systems feeding the grid providing a synthetic 'inertia' to the utility grid system.
Thank you. Clears up my concerns of spending money to have to use a warranty. I prefer to have a warranty and never use it.
 
Just choose the 12000 xp, 18K PV or Flexboss and don't worry about it, they can all handle this. I personally am running a pair of 18K PV for an all electric house in Florida, don't even think about the inverters anymore.
Good to hear. Thank you.
 
Just saw this, actually just testing the Power Pro indoor battery, but they were using the 18k PV to put the loads on it. screen on the 18K does not show it but I bet the data graphs caught it.
base load of 195 amps on the battery and 18 K outputting ~10KW.
Then they started that IR bellt drive compressor on top of the existing load, surging the single Power Pro battery and 18Ks abilities.

Not bad. Not bad at all.

 
Last edited:
More to add on the video above, versus my own test experience today with my air compressor.

Was wiring a disconnect input for the 18K from grid so the 18K can be taken out of the circuit, so it seemed like a good time to test whether the 18 K could handle the 80 gallon belt drive after being impressed by the video.

My results do not match the test they did above.

Had about a 3000 watt load on the 18K- with an additional 2KW coming in from PV, ( versus their 195 amps battery current draw already to support their existing loads with only one Power Pro, before they were able to successfully start the belt drive IR compressor)


I tried to start the 80 gallon two stage (6 hp start)- 5 HP running compressor and the compressor maybe rotated 1 revolution then Moaned and lights out.

The 18k shut down.

I immediately shut off the pressure switch on the compressor.

18K and lights came back up in about 5 seconds.


Now I have my answer, as far as ever running this compressor "Off Grid" without a soft start or adding another 18K PV the answer is no.
 
Last edited:
More to add on the video abpve versus my own test experience today with my air compressor.

Installed a disconnect for the 18K from grid so the 18K can be taken out of the circcuit so it seemed like a good time to test whether the 18 K could handle the 80 gallon belt drive.

My results do not match the test they did above.

Had about a 3000 watt load on the 18K with 2KW coming in from PV and the three Power Pros were connected, the Grid was disconnected.

I tried to start the 80 gallon Black Diamond two stage 5 HP compressor and the compressor maybe rotated 1 revolution and lights out.

The 18k shut down .

I imediately shut off the pressure switch on the compressor. 18K came back up in about 5 seconds.
Now I have my answer, as far as ever running this compressor without a soft start or adding another 18K PV the answer is no.
Have you measured the inrush current on the 80 gallon compressor before when it was wired into grid power?
 
Have you measured the inrush current on the 80 gallon compressor before when it was wired into grid power?
No I actually haven't, I do not have an inductive current meter that can catch and save a surge reading, but do have regular AC and DC inductive current ability on the meters. I will see what it shows.

Also in the 18K's defense- this compressor is marketed as a five HP (running) compressor the motor is actually a 6 HP / 24 amp unit.
After watching that video (starting their ("massive") compressor, was thinking maybe there is a chance... but knew there was also a good chance it would not. I do have a feeling that the two Schneider XW Pro 6848 Low Frequency transformer inverters in parallel I bought wouldn't flinch doing the same test.

I really do like the 18k PV, but as others have said, large inductive loads and or load imbalance are HF inverters nemesis when it comes to their perceived ratings.

Luckily our grid overall is pretty stable and the chances I would need to pump up the large compressor with grid down are slim anyway. I am always impressed when there is a lot of solar incoming and the 18K can be charging the batteries at 12KW and also knocking the grid use down by a few KW at the same time.
 

Attachments

  • PXL_20250309_004057381.MP~2.jpg
    PXL_20250309_004057381.MP~2.jpg
    169.1 KB · Views: 8
Last edited:
Lets look back in 10 years and see how many of what inverters are in land fills. I have my bets already placed. I'm putting all my chips on blue.
 
Lets look back in 10 years and see how many of what inverters are in land fills. I have my bets already placed. I'm putting all my chips on blue.

It will be interesting to see.

I may have to get an insight home unit on the way, so I can at least test the 2 XW's in parallel to see how they do at starting this compressor.
 
If I had to do it today. . . 2 12000xp's, pretty sure it would start your motor. That being said, . . . I'd soft start it or replace it with something more inverter friendly.
 