Tldr: lux12k, eg4 18k Carries ~200vdc on the grid lines in off-grid mode. Even in standby voltage is present. Be careful.
Not sure if this has been discussed before.
I was working on the grid splitter box pulling feeders to the outdoor disconnect (no grid here, but future proofing) I put the inverters in standby, turned pv off, and then checked the EPS terminals were off and no AC voltage present.
Went about my business and got a zap. Grabbed my tester, sure enough after checking, I found 60vdc on the grid terminals. So I re-enabled the the inverters and checked. ~200vdc live to ground/neutral.
I contacted lux and got a pdf in response saying that "this is normal, and not a shock hazard".
A couple things; I did get a shock, it wasn't my imagination. Voltage doesn't go to 0 under load - I have a constant 250w load and I've checked with a 2000w load. ~200vdc always present. My Inspector is going to raise hell about un-documented voltage sources being present on "dead" lines.
This is a hazard and should be documented in the manuals.
Not sure if this has been discussed before.
I was working on the grid splitter box pulling feeders to the outdoor disconnect (no grid here, but future proofing) I put the inverters in standby, turned pv off, and then checked the EPS terminals were off and no AC voltage present.
Went about my business and got a zap. Grabbed my tester, sure enough after checking, I found 60vdc on the grid terminals. So I re-enabled the the inverters and checked. ~200vdc live to ground/neutral.
I contacted lux and got a pdf in response saying that "this is normal, and not a shock hazard".
A couple things; I did get a shock, it wasn't my imagination. Voltage doesn't go to 0 under load - I have a constant 250w load and I've checked with a 2000w load. ~200vdc always present. My Inspector is going to raise hell about un-documented voltage sources being present on "dead" lines.
This is a hazard and should be documented in the manuals.