I'm having a strange problem with my SNA-US 6000 (aka 6000xp) inverter. I'm wondering if anyone's seen this before, or has any suggestions.
The behaviour is that once the PV has charged the batteries to full, the inverter keeps trying to flip operating mode from Solar/Battery to Grid mode. It'll do this sporadically, but frequently. By that, I mean it doesn't do it regularly on a timed schedule (e.g. every 30 seconds). But it does do it often, anywhere between 15 seconds to 5 minutes. The inverter is completely off-grid, so it immediately flips back to Solar/Battery mode. This flip/flop causes a brief power outage. I have a network UPS connected to the inverter's load circuit, so I know when this is happening because I can hear my UPS buzzer go off in response to the power interruption.
This only seems to happen when the batteries are fully charged, and the load is less than PV potential. For example, let's say that up until the batteries were full I was drawing ~2500w from PV. Once charging is no longer required, PVin drops to something close to my base load (~300watts), and this mode flipping behaviour starts happening. If I were to plug in my EV charger and draw an additional 2500w (combined ~2800w, more than PV potential) the inverter would no longer attempt to flip back and forth between solar/battery and grid modes.
I'm referring to the modes as "Solar/Battery" and "Grid" because those are the two modes Solar Assistant displays. The inverter itself doesn't really display a "mode", and you have to just infer what it's doing based on the icons and arrows on the LCD. The flip seems to happen so fast that the LCD doesn't display anything other than what looks like what the manual calls "PV+BAT Off-Grid". The fact that Solar Assistant briefly shows a different mode means that some modbus register is telling it otherwise though...
Some relevant notes:
Sorry this post turned out to be a long one... I'd really appreciate any guidance or suggestions anyone may have.
-A
The behaviour is that once the PV has charged the batteries to full, the inverter keeps trying to flip operating mode from Solar/Battery to Grid mode. It'll do this sporadically, but frequently. By that, I mean it doesn't do it regularly on a timed schedule (e.g. every 30 seconds). But it does do it often, anywhere between 15 seconds to 5 minutes. The inverter is completely off-grid, so it immediately flips back to Solar/Battery mode. This flip/flop causes a brief power outage. I have a network UPS connected to the inverter's load circuit, so I know when this is happening because I can hear my UPS buzzer go off in response to the power interruption.
This only seems to happen when the batteries are fully charged, and the load is less than PV potential. For example, let's say that up until the batteries were full I was drawing ~2500w from PV. Once charging is no longer required, PVin drops to something close to my base load (~300watts), and this mode flipping behaviour starts happening. If I were to plug in my EV charger and draw an additional 2500w (combined ~2800w, more than PV potential) the inverter would no longer attempt to flip back and forth between solar/battery and grid modes.
I'm referring to the modes as "Solar/Battery" and "Grid" because those are the two modes Solar Assistant displays. The inverter itself doesn't really display a "mode", and you have to just infer what it's doing based on the icons and arrows on the LCD. The flip seems to happen so fast that the LCD doesn't display anything other than what looks like what the manual calls "PV+BAT Off-Grid". The fact that Solar Assistant briefly shows a different mode means that some modbus register is telling it otherwise though...
Some relevant notes:
- I'm running the latest firmware on my inverter (1A1011)
- I'm running in open loop mode with voltage based charging. Absorb is set to 56.4v and float is set to 54v. I don't believe this is used by the inverter, but I've got the equalization voltage also set to 56.4v, and the interval set to 0 (which should disable equalization).
- My batteries are a pair of EG4 LLv2 48v 100AH. They're connected to Solar Assistant via RS485 for monitoring, but as I said I'm running in open loop mode so not connected to the inverter's BMS port.
- Since the inverter isn't connected to the grid, AC charging is disabled completely. Timeslots1/2/3 are all set to 0:00 - 0:00, grid-first is never, etc.
- Smart load is disabled, export to grid is disabled, AC coupling is disabled
Sorry this post turned out to be a long one... I'd really appreciate any guidance or suggestions anyone may have.
-A