More than one N/G bond creates a parallel path on the neutral and ground. Which makes the ground conductor and neutral conductor share the neutral current. Neutral current should never be carried by the ground conductor. (Only fault current)I am wondering why more than one ground connection within the house equipment is a bad idea ?
As long as the bonds and wire making those bonds are stout enough.
Now multiple ground rods outside I see the problem with voltage potential across the poor conductivity of the earth.
But across a 6/8/10 AWG copper wire inside ????