Hello all,
I'm having an issue with my pair of LV6548 inverters not recognizing my battery.
I've got (2) 24v 100AH Ampere Time batteries (https://www.amazon.com/gp/product/B08P6LP1J9/ref=ppx_yo_dt_b_search_asin_title?ie=UTF8&psc=1). These are wired in series (to get 48V) then connected to the inverters.
The inverters are giving a BP warning (which according to the manual is Battery Disconnected).
Settings Below
Option 5 = User Defined
Option 16 = Solar and Utility
Option 26 = 56.4V
Option 27 = 55.0V
Option 29 = 48.0V
The 1st night I had this hooked up, it appeared to work as it should. With option 1 set to SbU (solar then battery then utility), I could see it working. At night the load was coming from the battery, and the grid was charging the battery as well. I didn't think that was very efficient (just cycling through the battery), so I programmed option #16 to only charge the batteries off Solar. Well I don't have all my panels setup, so my load was always more then what I was producing so the batteries didn't charge.
Now I've changed setting #16 back to solar and grid and the batteries are just not charging. With a volt meter, I have tested that the wires are hot.
I feel like I must be missing something simple.
As a test, I also removed the Fuse / Shunt. Got the same results. Added them back in. Not sure how to troubleshoot at this point.
I think the battery is completely dead, and the inverters are not recognizing it to charge?
I'm having an issue with my pair of LV6548 inverters not recognizing my battery.
I've got (2) 24v 100AH Ampere Time batteries (https://www.amazon.com/gp/product/B08P6LP1J9/ref=ppx_yo_dt_b_search_asin_title?ie=UTF8&psc=1). These are wired in series (to get 48V) then connected to the inverters.
The inverters are giving a BP warning (which according to the manual is Battery Disconnected).
Settings Below
Option 5 = User Defined
Option 16 = Solar and Utility
Option 26 = 56.4V
Option 27 = 55.0V
Option 29 = 48.0V
The 1st night I had this hooked up, it appeared to work as it should. With option 1 set to SbU (solar then battery then utility), I could see it working. At night the load was coming from the battery, and the grid was charging the battery as well. I didn't think that was very efficient (just cycling through the battery), so I programmed option #16 to only charge the batteries off Solar. Well I don't have all my panels setup, so my load was always more then what I was producing so the batteries didn't charge.
Now I've changed setting #16 back to solar and grid and the batteries are just not charging. With a volt meter, I have tested that the wires are hot.
I feel like I must be missing something simple.
As a test, I also removed the Fuse / Shunt. Got the same results. Added them back in. Not sure how to troubleshoot at this point.
I think the battery is completely dead, and the inverters are not recognizing it to charge?