This will be an off grid run to the critical loads panel. Here are the output specs for the 6048WP from the manual:
Nominal Output Current 25A per phase
Inrush Current/Duration 30 A per phase / 20ms
Maximum Output Fault Current/Duration 90 A per phase / 1ms
Maximum Output Overcurrent Protection 90 A per phase
Power Factor Range 0.9 lead – 0.9 lag
The AC output of my LVX6048WP will be going to an off grid panel that would supply critical load during and outage, Was wondering if it would be best to use a 50amp double pole breaker or 25amp double pole breaker. The per phase part I guess is what's confusing me.
Nominal Output Current 25A per phase
Inrush Current/Duration 30 A per phase / 20ms
Maximum Output Fault Current/Duration 90 A per phase / 1ms
Maximum Output Overcurrent Protection 90 A per phase
Power Factor Range 0.9 lead – 0.9 lag
The AC output of my LVX6048WP will be going to an off grid panel that would supply critical load during and outage, Was wondering if it would be best to use a 50amp double pole breaker or 25amp double pole breaker. The per phase part I guess is what's confusing me.