Victron specifically says not to use ferrules (except on screw down terminals). You may cause increased resistance. The terminals for both Victron equipment (besides the connections that are for lugs) and IMO are clamping style terminals that compress the wires like a ferrule would to begin with. You should not be using ferrules for those connections like @AntronX mentioned. Signature Solar in their IMO video also shows not to use ferrules.I am using ferules on everything from 6 to 2 ga if it’s not a lug connection.. ( mainly Victron and IMO )
Victron specifically says not to use ferrules. You may cause increased resistance. The terminals for both Victron equipment (besides the connections that are for lugs) and IMO are clamping style terminals that compress the wires like a ferrule would to begin with. You should not be using ferrules for those connections like @AntronX mentioned. Signature Solar in their IMO video also shows not to use ferrules.
Well, EG4/manufacturer uses ferrules on those kind of terminals. So which way should it be?Don't use ferrules on those kind of terminals.
14AWG with 105C insulation is rated at 39A. https://www.coonerwire.com/amp-chart/So lets see if I am understanding this correctly. In the video it shows the scc is using 14 awg wire for the PV imput and eg4 thinks that is OK(because they are selling them in that configuration) for the rated 22 amps PV imput limit of the scc.
While I see the wire is rated at 105c I would prefer to turn the sun rays I go to the trouble and expense of collecting into stored energy instead of wasted heat.
Victron specifically says not to use ferrules (except on screw down terminals). You may cause increased resistance. The terminals for both Victron equipment (besides the connections that are for lugs) and IMO are clamping style terminals that compress the wires like a ferrule would to begin with. You should not be using ferrules for those connections like @AntronX mentioned.
I'll have to check that out, thanks.Signature Solar in their IMO video also shows not to use ferrules.
Now - IMO
Use the ferrules inside the box and get a replacement connection for that burned out one.
Did that, works fine.Replace the melted/burned wires.
Positive wire runs to circuit breaker, not much length there.Don't run the wire all the way to the board - tempting - but unless your solar wire is 105c it could cause issues.
I'm waiting to talk to SS on Monday, I don't have time to sit on hold for an hour this time of year.All the way to the board as a temporary thing is fine.
You are contradicting yourself, ferrules inside the box but not outside- same terminal on both sides. My opinion at this point is the factory side was loose, I checked the other SCC and those were not completely tight.
Checked the video, it isn't covered in the video, it just shows the lady not using a ferrule.Signature Solar in their IMO video also shows not to use ferrules.
That’s exactly what I have found with the several brands I bought…OK,
When to use ferrules and when not to use them.
Use them when -
The screw terminal just has the screw directly contacting the wire and the wire is fine stranded.
When the mfg calls for them
When not to use them -
On stranded THHN when the screw pushes on the wires directly unless the mfg calls for it
when the mfg says NO - like the victron MPPT
In any sort of spring push connection like wego unless they are called for
on any sort of solid wire.
Optional -
When the screw pushes down a plate that is cupped so that it gathers the stranded wire together - like the victron MPPT
When the screw pushes down a plate that is flat and the wires are not fine stranded (like thhn)
When the hole is a hex shape and cups the wires top and bottom
Ferrules are like everything these days - mfg in china - all of them for the most part.
Good ones are:
thin enough to deform with the crimper but NOT become crooked like a snake.
When they are crimped they are straight.
Long enough to bottom out on your socket
Bad ones are:
thin and when you crimp them they tear at any point
Not long enough to bottom out in the connection you are using them in - touching plastic is not bottoming out.
So thick they are super hard to crimp and they don't make a nice shape
Correct crimping technique -
strip the wire long enough to go all the way to the end of the ferrule and have the wire sheath inside the ferrule plastic
Push it all the way through and trim if needed.
Use the correct crimper - 4, 5 ,6 and 8 sided ones exist. For electrical stuff it will be the 4 or 6 sided typically. This depends on if the socket is a flat plate/screw or if it is the hex shapped socket.
If you need to trim after the crimp you probably didn't do something right - like it didn't fill the ferrule.
do NOT twist the wire before inserting - you want a cold weld type bond and twisting will cut strands.
it is permissable to double the wire back on itself, but discouraged.
And there are non-insulating ferrules that don't have the plastic bit. These are typically larger awg
It shouldn't deform the wire into a snake.
It shouldn't tear the metal of the ferrule
it should fill the ferrule completly before you crimp if it doesn't you will get a snake
Ferrules come in sizes like AWG and they are also in mm in metric. Just like crimpers they can be mismarked.
A good reliable source of ferrules is - you get what you pay for.
Ferrules Direct
Insulated Ferrules, Non-Insulated Ferrules, Terminals, Wire Ducts, Crimping Tools, Cable Accessories, Terminal Blocks, Push Buttons, Heat Shrink, Compression Lugs, Automotive Products, Wire Cutters, Wire Stripperswww.ferrulesdirect.com
Note - this is Navy training from 35 years ago so it might have changed.
That’s exactly what I have found with the several brands I bought…
Cheap ones suck ….good ones Do a good job…
I like that heat detector…I don’t have that unit …im Gona get one..Glad that was an easy fix. A bit unsettling. It’s always amazing how terminals tend to loosen with time. It’s primarily after the initial tightening and much less thereafter. Chinese DIN breakers are the worst offenders, but even these eventually stay snug. This does make me wonder about the factory side of my other equipment so this is eye opening and glad you posted this. This might be another time for me to mention that a combination photo/ionic smoke detector might be a good idea to install over the system and incorporated into the home’s smoke alarm network. It’s very easy to tie in.
Using a dual mode detector sets off absolutely the earliest possible alarm because of the different types of burning or smoldering affects different sensors. I installed a heat detector also but in truth I think the multi sensor smoke detector is all that’s needed based on excellent sensitivity. It has gone off several times but it was my own fault because different types of heat related particle producing activities that I was doing in the vicinity. I guarantee that cooked wire would have set off one of those sensors. Both are of these are actually First Alert View attachment 213367
Yes…yes…yess…yess. It has a half life of 4-7 hours leaving the body in normal air ..with enough in ya over the correct timeline and % you will be dead unless you get to medical help. Even if you feel sorta ok…Carbon monoxide is accumulative and takes an amazing amount of time to leave the body, so if you’re working on or around engines every day……..
Normally you have one carbon monoxide detector centrally located, but all my detectors were old and just replaced all them in the living space the monoxide/smoke detectors. Figured one is bound to work if it’s there. Combustible vapor detectors do have a limited life expectancy once you put it in service. Follow the manufacturer instructions for testing and replacement intervals. I had four of them in the boat I owned. Combustable vapors are heavier than air and settle to the lowest spaces so you place them as low as possible without them being in danger of contracting normal water levels.
View attachment 213393
Now - IMO
Use the ferrules inside the box and get a replacement connection for that burned out one. Replace the melted/burned wires.
Don't run the wire all the way to the board - tempting - but unless your solar wire is 105c it could cause issues.
Actually all the way might be best.All the way to the board as a temporary thing is fine.