I have a Kubota Lowboy II GL11000 diesel generator rated for 10,000 watts (yes, watts, not kVa) continuous output (surge up to 11k). It has a 240v CS6369 output terminal, rated for 41.7a at 240v.
Primary use will be to charge batteries, currently 4 MNPowerflo16s, as needed during the winter, supplementing 19,200w of solar panels.
In order to run the generator around 80% of it's rated capacity, I'm figuring on running 2 Chargeverters outputting 54v 82ish amps each which translates to a 16.5a draw at 240v on the generator per chargeverter, so a total draw of 33ish amps at 240v on the generator. That should be around 80% output.
Question is, can I just build/wire a Y splitter off a CS6369 plug to 2 female L18-30P plugs? So 2 wires to each terminal on the CS6369 one of each running out to a L18-30P?
Primary use will be to charge batteries, currently 4 MNPowerflo16s, as needed during the winter, supplementing 19,200w of solar panels.
In order to run the generator around 80% of it's rated capacity, I'm figuring on running 2 Chargeverters outputting 54v 82ish amps each which translates to a 16.5a draw at 240v on the generator per chargeverter, so a total draw of 33ish amps at 240v on the generator. That should be around 80% output.