I am getting ready to make the connections between 1 GridBOSS, 3 FlexBOSS21s, and 4 EG4 Outdoor wall mount batteries. I noticed the following line in the FlexBoss manual:
"When installing multiple inverters in parallel, it is recommended to use equal length AC cables from each inverter to the main panel and from each inverter to the loads panel. This helps ensure the load sharing between each inverter is as even as possible."
How important is this? Because of the spacing of the batteries, that would be quite a bit of 2AWG wire coiled up in the conduit boxes. If I use the length for the furthest FlexBOSS then the next furthest would be 3-1/2 feet and the closest would have about 7 feet of excess wire.
"When installing multiple inverters in parallel, it is recommended to use equal length AC cables from each inverter to the main panel and from each inverter to the loads panel. This helps ensure the load sharing between each inverter is as even as possible."
How important is this? Because of the spacing of the batteries, that would be quite a bit of 2AWG wire coiled up in the conduit boxes. If I use the length for the furthest FlexBOSS then the next furthest would be 3-1/2 feet and the closest would have about 7 feet of excess wire.