I'm going to start off by saying I've spent almost 24 hours deciding whether or not to post this. It's embarrassing, I knew better, and I made the very human decision to put off something I "thought would be ok" because winter arrived. I'm choosing to share this because I came here to learn and perhaps provide something of value to others, as many here have done for me.
Brief backstory: I put my system, including a small set of panels live, late last September. The string in question is an 8s2p set of 325W panels, 8 on ground mounts, 8 vertically mounted on the back of my pole barn. When I wired it, I shortcut making sure the MC4 connections were properly protected, especially the 2-1 combiners I used. A recent storm + high winds dislodged them from my ill-advised 'I'll get to that in the spring' hack. Yesterday, we had fresh snow on the ground, very cold temps, and very bright sun. High voltage + 18-20 amps under load.
If my wife hadn't been home with a day off, I'm not sure how far this would've gotten. I work from home, but wouldn't have seen this right away. She spotted smoke and these connectors on fire.



Note that some of that dirt ended up there as a result of getting this put out, but these connectors were exposed. THEY SHOULD NEVER HAVE BEEN LEFT THIS WAY.
I have a guess as to what happened. I don't know for sure. Storm came through, my connections/combiners ended up on the ground. We had that 'perfect storm' of conditions that produced high output yesterday: cold, bright + reflective. Connections heated up, melting the snow, arced/shorted. The result is in the pictures above. Solar Assistant shows that even as this event was underway, there was enough of a connection to produce voltage. There was a very brief spike/surge in amperage, otherwise it appeared normal. Assuming that data is accurate, had each of these strings terminated in/at a fuse (as they are now), the fuse likely would've done its job.
Please, please please:
Use my embarrassment to save yourself the same, or worse. Be safe, and take nothing for granted, my fellow photon harvesters.
Brief backstory: I put my system, including a small set of panels live, late last September. The string in question is an 8s2p set of 325W panels, 8 on ground mounts, 8 vertically mounted on the back of my pole barn. When I wired it, I shortcut making sure the MC4 connections were properly protected, especially the 2-1 combiners I used. A recent storm + high winds dislodged them from my ill-advised 'I'll get to that in the spring' hack. Yesterday, we had fresh snow on the ground, very cold temps, and very bright sun. High voltage + 18-20 amps under load.
If my wife hadn't been home with a day off, I'm not sure how far this would've gotten. I work from home, but wouldn't have seen this right away. She spotted smoke and these connectors on fire.



Note that some of that dirt ended up there as a result of getting this put out, but these connectors were exposed. THEY SHOULD NEVER HAVE BEEN LEFT THIS WAY.
- I have all the conduit in my garage to properly trench and bury my wire.
- I have a combiner box, with fusing and breakers.
- I have this forum, prior warning from others, and at least one other thread on this kind of issue to reference.
I have a guess as to what happened. I don't know for sure. Storm came through, my connections/combiners ended up on the ground. We had that 'perfect storm' of conditions that produced high output yesterday: cold, bright + reflective. Connections heated up, melting the snow, arced/shorted. The result is in the pictures above. Solar Assistant shows that even as this event was underway, there was enough of a connection to produce voltage. There was a very brief spike/surge in amperage, otherwise it appeared normal. Assuming that data is accurate, had each of these strings terminated in/at a fuse (as they are now), the fuse likely would've done its job.
Please, please please:
- Respect your PV array(s), the voltage (and amperage under load) that is generated.
- Check your crimps. Use the tools to make sure the MC4 is completely tight.
- Plan for the extreme/worst case/'nah, this will never happen (to me)' conditions.
- Make sure anyone living where your system is running knows:
- To call 911 (kids)
- Knows where the fire extinguishers are (you have some, right?)
- Knows how to shut the system down safely (do a walkthrough, keep a simple how-to sheet in critical areas)
- Use the stuff you buy. Don't wait -- unless waiting means putting off commissioning a new string/array/system until you're fully ready.
- Where possible, regularly inspect these connections.
- Don't be lazy like me. Seriously. Don't.
Use my embarrassment to save yourself the same, or worse. Be safe, and take nothing for granted, my fellow photon harvesters.