I read about parallel batteries, and I am of the belief that it is ok to mix capacity with same voltage/chemistry.
I have a Sol-Ark 15k with 6 new 5.12kWh Endurengery batteries (30.72kWh) in closed loop. I needed an "installed" system for the Energy Storage Solutions (f/k/a Connected Solutions). But, nothing stops me from "enhancing" the system.
I'm thinking of building a DIY battery with 280ah EVE batteries. I can get them for about $2,600 including BMS.
FWIW: the rack batteries are in 2 rack cases holding 3 batteries each, both cases connected to a bus-bar, that is then connected to the 2 battery connections of the sol-ark (DIY battery would also be connected to the bus bar). So, in some respects, it would be two 15kWh racks plus a 14.6kWh DIY. While the "banks" are close to equal, the batteries in parallel are really One 14.6kWh battery and Six 5.1kWh batteries.
The question is: Any thoughts on what would happen if I kept the Six Endurenergy batteries in closed-loop with the Sol-Ark, with the DIY battery also connected?
While the SOC that Sol-Ark receives via closed loop is 50% off with respect to remaining energy (does not take into account the DIY battery), does it really matter? Sol-Ark will keep taking power until SOC reaches the set lower limit.
Which would you do: Use the closed-loop for SOC, or go with Sol-Ark calculation of SOC (use voltage to cutoff)?
I have a Sol-Ark 15k with 6 new 5.12kWh Endurengery batteries (30.72kWh) in closed loop. I needed an "installed" system for the Energy Storage Solutions (f/k/a Connected Solutions). But, nothing stops me from "enhancing" the system.
I'm thinking of building a DIY battery with 280ah EVE batteries. I can get them for about $2,600 including BMS.
FWIW: the rack batteries are in 2 rack cases holding 3 batteries each, both cases connected to a bus-bar, that is then connected to the 2 battery connections of the sol-ark (DIY battery would also be connected to the bus bar). So, in some respects, it would be two 15kWh racks plus a 14.6kWh DIY. While the "banks" are close to equal, the batteries in parallel are really One 14.6kWh battery and Six 5.1kWh batteries.
The question is: Any thoughts on what would happen if I kept the Six Endurenergy batteries in closed-loop with the Sol-Ark, with the DIY battery also connected?
While the SOC that Sol-Ark receives via closed loop is 50% off with respect to remaining energy (does not take into account the DIY battery), does it really matter? Sol-Ark will keep taking power until SOC reaches the set lower limit.
Which would you do: Use the closed-loop for SOC, or go with Sol-Ark calculation of SOC (use voltage to cutoff)?