OK, I have put together a new DIY combiner box plan. This should accommodate 6 in 2 out, and work for my 5S2P going to Input 1 on the LV6548, and the 5S3P going to input 2. I found these on Amazon and I think two of them in an off-the-shelf PVC box may just do the trick. They can handle 600V and 12A per string going in. I'm hitting them with 188Voc and 8.27A per string. And they're rated for 600V/36A going out. I should have 188Voc and 24.81A heading to input 2 and 188Voc and 16.54A heading to input 1 :
Dinkle Solar Combiner Box 3 Fused 10 AWG Inputs 6 AWG Output 36A 600V: Amazon.com: Industrial & Scientific
www.amazon.com
And these are the fuses I ordered, which I'm pretty sure spec out to work:
I think I'll wait to see what sort of box will work the best for these, and will hopefully be able to get that locally when I see what it all looks like. This should end up costing about the same and maybe less than handling it with branch connectors and in-line fuses, and it puts all the connections in one waterproof box instead of strewn out every place.
It's surprising to me there are not more suitable off the shelf PV combiner boxes ready to go for this size system. I guess it's sort of in between the options. Or maybe I just missed some obvious solutions. Everything I found either didn't spec out, or was WAY overkill and very expensive.
Wish me luck!!