I need to add OCPD's to my (indoor) battery system as my EG4 18kPV's are outdoors about 25 feet away. The most straightforward approach seems to be to install class T fuses in the EG4 conduit boxes.
Because the conduit boxes are open at the bottom and assemble to the tops of the batteries I think they meet the Code definition of electrical "enclosure" (where fuses can be installed) rather than "raceway". Also the boxes are pretty big so should meet device and conductor volume requirements.
So I think it ought to be Code compliant to install fuses in them. Anybody tried this or something similar and/or found any Code or other practical issues that would preclude this approach?
Some (planned) details. 4 x EG4 indoor wall mount batteries with indoor conduit boxes mounted. 4, 250a fuses protecting both + and - 4 awg cables to each inverter, one mounted in each conduit box. Two batteries connected in parallel at each fuse using the supplied 2 awg EG4 battery conductors. I'm on NEC 2017.
Thanks!
Because the conduit boxes are open at the bottom and assemble to the tops of the batteries I think they meet the Code definition of electrical "enclosure" (where fuses can be installed) rather than "raceway". Also the boxes are pretty big so should meet device and conductor volume requirements.
So I think it ought to be Code compliant to install fuses in them. Anybody tried this or something similar and/or found any Code or other practical issues that would preclude this approach?
Some (planned) details. 4 x EG4 indoor wall mount batteries with indoor conduit boxes mounted. 4, 250a fuses protecting both + and - 4 awg cables to each inverter, one mounted in each conduit box. Two batteries connected in parallel at each fuse using the supplied 2 awg EG4 battery conductors. I'm on NEC 2017.
Thanks!