cells connected in parallel doesn't balance them.
Cells connected in parallel and charged part way past knee of the curve is what balances them. Typically to 3.65V.
That's parallel top balancing.
Got a BMS (or two)?
You'll need that when you series charge them.
10 panels in series x 42.04Voc = 420.4V. That is too close to 450V, just 7% rise due to cold temperature and it will exceed 450V.
You need about 16% headroom. To compute that exactly, we need:
1) Temperature coefficient of Voc from PV panel data sheet.
2) Record coldest temperature for your location.
Cells connected in parallel and charged part way past knee of the curve is what balances them. Typically to 3.65V.
That's parallel top balancing.
Got a BMS (or two)?
You'll need that when you series charge them.
10 panels in series x 42.04Voc = 420.4V. That is too close to 450V, just 7% rise due to cold temperature and it will exceed 450V.
You need about 16% headroom. To compute that exactly, we need:
1) Temperature coefficient of Voc from PV panel data sheet.
2) Record coldest temperature for your location.