NationalGrid clearly states that you can't connect a PV inverter to the grid unless it is UL listed.
The MPP LV 5048 is not UL listed. It is only CE listed.
Have I misread the NationalGrid requirements?
There does not seem to be any wiggle room. The spec does not seem to care if the LV 5048 promises to not feed power back into the grid. The blocker is 'UL listed/certified'.
Is there an "enforce PV safety" box that I can buy that is UL certified that safely flows the grid power in one direction into the LV 5048?
EDIT: Actually if the box is UL certified then I probably don't care if we are feeding power back into the grid as the box will ensure it is done safely (prevent PV power from feeding the grid if the grid is down for maintenance etc..)
All inverter-based solar PV projects 100 kW or less with applications submitted on or after June 1, 2018 are subject to ISO-NE Ride through Requirements.
Oddly they provide a MS Word document in the section, "Effective June 1, 2018"
which contains, "To comply with the ISO-NE Ride-through requirements, inverters in solar PV installations shall be certified per the requirements of UL 1741 SA as a grid support utility interactive inverter, and have the voltage and frequency trip settings and ride-through capability described in the ISO-NE Inverter Sources Requirements Document."
* Some more references:
-> be certified per the requirements of UL1741SA as a grid support utility interactive inverter
* A very detailed document explaining DG requirements:
The specific combination of these factors will determine if any system study requirements are needed. The following are some examples of the items that may be considered under this screen:
-> Does the Generating Facility utilize UL 1741/IEEE 1547 Certified anti-islanding functions and equipment? (LV 5048 == no)
The MPP LV 5048 is not UL listed. It is only CE listed.
Have I misread the NationalGrid requirements?
There does not seem to be any wiggle room. The spec does not seem to care if the LV 5048 promises to not feed power back into the grid. The blocker is 'UL listed/certified'.
Is there an "enforce PV safety" box that I can buy that is UL certified that safely flows the grid power in one direction into the LV 5048?
EDIT: Actually if the box is UL certified then I probably don't care if we are feeding power back into the grid as the box will ensure it is done safely (prevent PV power from feeding the grid if the grid is down for maintenance etc..)
All inverter-based solar PV projects 100 kW or less with applications submitted on or after June 1, 2018 are subject to ISO-NE Ride through Requirements.
Oddly they provide a MS Word document in the section, "Effective June 1, 2018"
which contains, "To comply with the ISO-NE Ride-through requirements, inverters in solar PV installations shall be certified per the requirements of UL 1741 SA as a grid support utility interactive inverter, and have the voltage and frequency trip settings and ride-through capability described in the ISO-NE Inverter Sources Requirements Document."
* Some more references:
-> be certified per the requirements of UL1741SA as a grid support utility interactive inverter
* A very detailed document explaining DG requirements:
The specific combination of these factors will determine if any system study requirements are needed. The following are some examples of the items that may be considered under this screen:
-> Does the Generating Facility utilize UL 1741/IEEE 1547 Certified anti-islanding functions and equipment? (LV 5048 == no)