I am brand new to solar and electricity, but have done a lot of research, design, planning, and want to be as safe as possible. Have been lurking the forum for a while but this is my first post. Any insight will help me out tremendously.š
Setup:
Solar Array - 6 panels in 3 series 2 parallel 1500W total
Inverter - MPP Solar LV6548
No batteries yet
I don't have my battery cells yet, so just testing out the solar panels and inverter for now. Inverter is powered by 120VAC utility and solar array. I have the AC input plugged into a standard US wall outlet, and AC output on an extension cable. Wiring diagram and pictures below:


Some Inverter Settings:
The inverter restarts with small loads when the AC power is disconnected. I have seen it work with up to 400W, and stop working at as little as 100W. The inverter alone runs fine on just solar with no load. Have been testing this 12 pm - 3pm with full sun on the panels. I have utility power connected, and the solar array outputting 100V, confirmed with multimeter. I tried both yanking the AC power with load connected, and also connecting load with AC already disconnected. Once AC power is removed, the AC output is disabled and the inverter restarts. The issue seems to be with the inverter? Did I fry my inverter somehow? Am I expecting too much from the panels, and the occasional cloud is reducing output to less than 100W?
Things I tried:
Setup:
Solar Array - 6 panels in 3 series 2 parallel 1500W total
Inverter - MPP Solar LV6548
No batteries yet
I don't have my battery cells yet, so just testing out the solar panels and inverter for now. Inverter is powered by 120VAC utility and solar array. I have the AC input plugged into a standard US wall outlet, and AC output on an extension cable. Wiring diagram and pictures below:


Some Inverter Settings:
- Output Source Priority: Tried 'Solar Utility Battery' and 'Utility Solar Battery'
- AC Input Range: Tried both 'Appliance' and 'UPS'
- Bypass Function: Tried 'Disabled' and 'Enabled'
- Over Temperature Auto Restart: Disabled
- Overload Auto Restart: Disabled
The inverter restarts with small loads when the AC power is disconnected. I have seen it work with up to 400W, and stop working at as little as 100W. The inverter alone runs fine on just solar with no load. Have been testing this 12 pm - 3pm with full sun on the panels. I have utility power connected, and the solar array outputting 100V, confirmed with multimeter. I tried both yanking the AC power with load connected, and also connecting load with AC already disconnected. Once AC power is removed, the AC output is disabled and the inverter restarts. The issue seems to be with the inverter? Did I fry my inverter somehow? Am I expecting too much from the panels, and the occasional cloud is reducing output to less than 100W?
Things I tried:
- Confirmed polarity is correct on all panel wires, and double-checked they are hooked up properly per my diagram.
- At first I was confused my clamp meter was showing low amps on the solar panel wires. I realized that is normal when no load is connected, because the amps and watts only go when the loads are connected and current is able to flow. The clamp meter shows roughly 5 amps on the panels when I had around 500W load connected to utility through the inverter. With the array showing 100V, that math checks out to me. The inverter confirms this with the panels outputting roughly 500W. I presume if I connected more loads I would see nearly the 1500W max of the array. I should probably check that next.
- None of the wires feel hot.
- Inverter alarm sometimes not always shows LINE_FAIL when the AC gets pulled. Also shows 'Battery Under Shutdown' and 'Eeprom Fault' at seemingly random times.