MPP LVX-6048 Settings youre using

Thanks for starting this thread. Please try to keep it active. I'm waiting for someone to post parameters using eg4 lifepo
I love the comradery going on to help stormsoul out, but this is not the thread for that conversation. Stormsoul, please start a new thread with these questions on it. If I could copy and paste it all and start a new thread I would do that, but I dont think I have the ability to
 
I want to keep to the Facts, first list inverter and battery, then what settings are you using, then comment if there is any issue with those settings.
If you dont have the settings for a LVX-6048 or similar inverter, please dont post commentary. System description first, settings second, comments last.

I'll go first:

MPP LVX-6048
Trophy 100AH battery
6kw solar panels
Generator input

01-SbU
02-APL
03-120v
04-60
05-bLU
06-byd
07-LtE (there are symbols used, that a keyboard can not make so using next closest)
08-ttE
09-Gtd
10-SNU
11-100
13-20
14-USE
17-57.6
18-54.4
19-40.8
20-52
21-56.0
22-ESP
23-LON
24-bON
25-AOF
27-FEN
28-SIG
29-ntt
30-00:00
31-00.0
32-00.0
33-00.0
34-default
95-99 set to current time

Tell me yours and comments on mine vs yours
Getting low battery fault. Inverter not connecting to grid as backup 15kw felicity Battery
01 SBU
02 APL
03 120
04 60
05 BLU
06 BYE
07 LRD
08 TRD
09 GRD
10 OSO
11 60
13 30
14 USE
17 57.6
18 57.6
19 48
20 46
21 57
22 ESP
23 LON
24 BON
25 AON
27 FEN
28 SIG
 
LVX6048
15KW Felicity Battery
12/385 solar panels
Want my inverter to cutoff to utility when battery gets low and wait for solar. Its that getting fault 4. Her are my parameter
01 SBU.
02 APL.
03 120.
04 60.
05 BLU
06 BYE.
07 lrd.
08 lrd.
09 grd.
10 OSO.
11 60.
13 30.
14 USE
17 57.0
18 55.0
19 40.8
20 50.0
21 54.0
22 ESP
23 LON
24 BON
25 AON
27 FEN
28 SIG
29 ARE

Can someone help me with these parameters Thanks
 
Last edited:
Hello vcruz28. Since fault 4 is being triggered, voltage must be going below setting #19 (low DC cut off / 40.8volts). Since you also have #20 set to 50.0volts (stop discharging) I just guessing that it never is between 40 .8 and 50 volts... maybe the BMS in the battery is cutting off at 51 volts or something so volts jump to 0 volts causing the fault 4 without the opportunity for setting #20 to return you to grid. What is the SOC / voltage on the battery when you see the fault 4 ?
 
LVX6048
15KW Felicity Battery
12/385 solar panels
Want my inverter to cutoff to utility when battery gets low and wait for solar. Its that getting fault 4. Her are my parameter
01 SBU.
02 APL.
03 120.
04 60.
05 BLU
06 BYE.
07 lrd.
08 lrd.
09 grd.
10 OSO.
11 60.
13 30.
14 USE
17 57.0
18 55.0
19 40.8
20 50.0
21 54.0
22 ESP
23 LON
24 BON
25 AON
27 FEN
28 SIG
29 ARE

Can someone help me with these parameters Thanks
Change Settings:

#1 - SUB
#10 - SNU
#19 - 48
#20 - 51

Make sure battery charges to voltage above 52 volts.

Then change setting back #1 to SBU and #10 to OSO. I would keep #19 at 48 and #20 at 51, but change if need.
 
Change Settings:

#1 - SUB
#10 - SNU
#19 - 48
#20 - 51

Make sure battery charges to voltage above 52 volts.

Then change setting back #1 to SBU and #10 to OSO. I would keep #19 at 48 and #20 at 51, but change if need.
Thanks will be getting back with results
 
Change Settings:

#1 - SUB
#10 - SNU
#19 - 48
#20 - 51

Make sure battery charges to voltage above 52 volts.

Then change setting back #1 to SBU and #10 to OSO. I would keep #19 at 48 and #20 at 51, but change if need.
Thanks will be getting back with results
 
Hello vcruz28. Since fault 4 is being triggered, voltage must be going below setting #19 (low DC cut off / 40.8volts). Since you also have #20 set to 50.0volts (stop discharging) I just guessing that it never is between 40 .8 and 50 volts... maybe the BMS in the battery is cutting off at 51 volts or something so volts jump to 0 volts causing the fault 4 without the opportunity for setting #20 to return you to grid. What is the SOC / voltage on the battery when you see the fault 4 ?
Thanks will be getting back with results
 