Just finished an upgrade to my system to optimise things a little.
The goals I had were:
1a) I put in a supercap bank in between the inverter/charge and the BMS. This allows the caps to absorb the excess charge when the BMS goes to high disconnect. I put power diodes in to allow power into the caps quickly but discharge goes via a large resistor to keep the current down to an acceptable level. Super Caps
1b) I also put a contactor in to turn off the PV to the chargers
1c) I installed a large TVS diode across the MPPs (probably not required)
2) I am using the relay on a victron BMV-700 to control the PV contactors which can be set to any SOC or voltage.
3) I paralleled the on/off switch on the slave MPP unit to a relay which is turned on timer relay which in turn is turned on by a current sensing relay which monitors the AC current coming out of the inverters. So you can turn on the second MPP unit when a certain level of current is reached. Mud map of electrical box
electrical box
4) I install DPDT switches to allow me to put panels between my house or shed system PV panel transfer box
The goals I had were:
- Prevent the BMS from shutting the inverter down when it goes to high disconnect. Voltage spike caused by BMS shutting down high currents tripped the inverter occasionally.
- Charge lithiums to SOC not voltage so I can stop charging at say 80% SOC whilst charging at 100% voltage.
- Automatically turn on and off second 5kw inverter to save on standby power use.
- Flexibly share panels between two systems (this was done A while ago)
1a) I put in a supercap bank in between the inverter/charge and the BMS. This allows the caps to absorb the excess charge when the BMS goes to high disconnect. I put power diodes in to allow power into the caps quickly but discharge goes via a large resistor to keep the current down to an acceptable level. Super Caps
1b) I also put a contactor in to turn off the PV to the chargers
1c) I installed a large TVS diode across the MPPs (probably not required)
2) I am using the relay on a victron BMV-700 to control the PV contactors which can be set to any SOC or voltage.
3) I paralleled the on/off switch on the slave MPP unit to a relay which is turned on timer relay which in turn is turned on by a current sensing relay which monitors the AC current coming out of the inverters. So you can turn on the second MPP unit when a certain level of current is reached. Mud map of electrical box
electrical box
4) I install DPDT switches to allow me to put panels between my house or shed system PV panel transfer box