The generator I have is a Genergy Creta Sol, designed to attach to solar inverters.
Solarpower is the name of the software that is used to change the main settings of the Inverter (comes with the Inverter). This is needed as SolarAssistant can not change these settings (yet) Grid Tied/ Grid Tied with backup /Off-Grid.
My Settings are set to Off Grid with backup (III).
If anyone cares to look at the attached manual just to see if you can figure it out, please feel free to do so. This would be a great help to me.
There are virtually no information in the manual on how to set settings for a backup generator,
This is how I expected my setup to perform but as I said previously, I seem to have got nowhere with it.
Solar panels (5kw) worth generates power to my Inverter which is a 5KW Hybrid.
Attached is Pylontec 10.7kw batteries,
When my load exceeds 5kw, it switches to the grid then continues to charge batteries with Solar PV.
Once the load is reduced, it powers the loads with Solar PV and continues to charge batteries.
When Solar PV is unavailable, batteries power the load until depleted then the load is powered by grid.
What I expected it to do was:
During the day, Solar PV powers the load but if the 5Kw load is exceeded, the generator would start and power the load up to 7.5kw (Genergy Creta Sol 7500w). This does not happen, if the load exceeds it, again reverts to grid power. In the evening with no PV, the batteries would power the load until it reaches its set voltage (47v) ish. The inverter does stsrt automatically at this point but does not charge the batteries but powers the load. I seem to think that at this point many months ago,I isolated the Grid but Im not too sure.
Am I correct in thinking that this is how it should work, as above?
I haven`t seen the Generator OR the grid charge my batteries yet. I would need to check if my settings are set to charge with PV only. (I`m now thinking this may be the case)
If anyone has any Ideas this would be very helpful. Thanks in advance