multiplus-ii and PACE bms

Joined
Jan 3, 2024
Messages
65
Location
Great Britain
Hi I am just setting up my new prebuilt fogstar LiFePo4 battery , 48v 15.5kwh , eve cells , PACE BMS & JK Active Balancer

Fogstar battery link


I am connecting it to my Multiplus-ii 48/10000 , I have not got a Cerbo or any victron connectivity systems

I've spoke to fogstar they said to follow these instructions , but I don't understand how or where I get the Battery BMS to communicate with the multiplus . It says the BMS needs to send a signal to the inverter to tell it when to stop charging

How does this work ? Can anyone point me in the right direction please



 
The only way to make a BMS COMMUNICATE with a Victron inverter via the protocols mentioned is with a GX device. The communication entails telling the system what the Charge Voltage Limit (CVL), Charge current limit (CCL) and discharge current limit (DCL) and gives the BMS control of the GX connected devices.

What you have are the instructions for simple triggering the MP's inputs.

Your battery must have a relay that can open and close based on BMS trigger events - preferably TWO for charge/discharge separately. You must connect this relay(s) as described in the document, properly configure the battery relay behavior and load/configure the assistant.

Basically, the BMS keeps the circuit closed when everything is fine and opens it when it wants to disable charge, discharge, or both.

Sounds like you're getting some really crappy support. Based on the manual, I don't see that the battery can communicate with the inverter via the two-signal BMS method as it has no contactors/relays. You MIGHT be able to open the battery up and find something on the BMS itself.

From the manual:

1743721276227.png

You need a GX device and connect via the CAN port for battery communications.
 
Last edited:
The only way to make a BMS COMMUNICATE with a Victron inverter via the protocols mentioned is with a GX device. The communication entails telling the system what the Charge Voltage Limit (CVL), Charge current limit (CCL) and discharge current limit (DCL) and gives the BMS control of the GX connected devices.

What you have are the instructions for simple triggering the MP's inputs.

Your battery must have a relay that can open and close based on BMS trigger events - preferably TWO for charge/discharge separately. You must connect this relay(s) as described in the document, properly configure the battery relay behavior and load/configure the assistant.

Basically, the BMS keeps the circuit closed when everything is fine and opens it when it wants to disable charge, discharge, or both.

Sounds like you're getting some really crappy support. Based on the manual, I don't see that the battery can communicate with the inverter via the two-signal BMS method as it has no contactors/relays. You MIGHT be able to open the battery up and find something on the BMS itself.

From the manual:

View attachment 289790

You need a GX device and connect via the CAN port for battery communications.

Thank you for getting back


Is it safe to just run without communications ?
 
Honestly just buy a Cerbo (mine was an unsued unit from ebay - £140)
It's tempting !

I think they're a load of cables I need to buy too though @sunshine_eggo very kindly explained it all in detail in this thread:---



 